ChrisElectrical88

-
Mentor
Esteemed
Arms
Reaction score
1,650
Christ Im now as bad as the others.

Doing a EICR today and every bloody smoke detector was installed about 100mm away from the light. Conventional FA System with series 65 Smokes and Heats. I know building regs say 300mm distances from lights and walls. I know Aico mains smokes instructions say 300mm from walls and lights but I can’t find Series 65 instructions online or anything in 7671. Ita more to note it than code it as the fire alarm bloke should be picking it up on his 6 monthly inspections but isn’t.
 
Just put it as a comment on the EICR, no code, just a written comnent, bonus points if you can pull something over from the relevant 5839 part/clause.

While not part of the EICR, you're CYA by noting and directing, even though it's not on the 7671 scope, doesn't mean we shouldn't be pointing to the proper bits where relevent
 
Just put it as a comment on the EICR, no code, just a written comnent, bonus points if you can pull something over from the relevant 5839 part/clause.

While not part of the EICR, you're CYA by noting and directing, even though it's not on the 7671 scope, doesn't mean we shouldn't be pointing to the proper bits where relevent

Im hoping someone will tell me where in 5839 to look so I can stick it in the notes ?. Cause I can’t find it for love nor money
 
Maybe the Fire Alarm bloke is picking it up and noting it to CHA, but no-one is taking any notice or doesn't want to spend.

Found this here, damn beaten to it,


View attachment 59479
The fire alarm bloke isn’t, this HA don’t mess about, if there told something needs doing it’s just go ahead. He also hasn’t noted the supply is wired in twin and earth, it’s wired on the same circuit as several other items, it’s got no fire alarm do not switch off stickers, it’s got no double pole isolation.
My knowledge of fire alarms is limited as you might be able to tell, but I’m sure I’m right that the above items all need attention.
 
Sounds par for the course fitted by someone who probably has never seen BS5839:1.
[automerge]1594827468[/automerge]
For a Part 1 system it is 500mm from walls and similar obstructions.
 
Last edited:
Some photos of the lighting circuit on the EICR I found. Didn’t get a R1+R2 at every point surprisingly enough.
 

Attachments

  • E759D9CF-855F-4F6B-A00A-D8093604C3E9.jpeg
    137.4 KB · Views: 36
  • EF95891D-5468-41EC-A0CC-290B79DB71D3.jpeg
    68.1 KB · Views: 36
  • 8D2BFFEB-F7D7-4244-8472-7728DEC7190C.jpeg
    104 KB · Views: 38
  • 6226A1C2-4EFE-4428-832D-5F4A14E99F77.jpeg
    94.3 KB · Views: 37
  • C6714DF2-9CEC-4A02-847D-E4BB3BA6A365.jpeg
    255.3 KB · Views: 36
  • 8F44A896-EC4C-4235-9F6B-16C01A73B8C1.jpeg
    118.7 KB · Views: 36

Reply to EICR Smoke Detectors in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hi My 4 bed 2 storey house was extended 2 years ago and completely re-wired, but I am having to upgrade the insulation and board out the loft...
Replies
0
Views
1K
Hi Guys, Perhaps an odd question but maybe it has been pondered by someone before; Scotland newbuild timber framed house. As required hard wired...
Replies
17
Views
2K
I am an electrical labourer currently doing my own research on Alarms to self-educate as much as I can. I would like to state the general rules I...
Replies
15
Views
2K
Hi all, we got an EICR report done before tenanting our previous home having become "accidental landlords". See attached. The report came back...
Replies
12
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock