So the guidelines are to test,inspect 100% of bonding, if you see bonding in cu but can't see to test, just been to one and it was under the floor, would u class this as satisfactory or unsatisfactory, or just put at n/v and limitation?
 
Yes but it was 1.56ohms and I think the bonding is under the floor, so I did it on the nearest incoming tap, what would you do?

You need to make an assessment of whether that is acceptable or not.
Is the bonding connection accessible? Is the impedance you measured right for the estimated length of the bonding conductor? Does the pipe work test out as an extraneous part? Did you disconnect all parallel paths before testing?
 
You need to make an assessment of whether that is acceptable or not.
Is the bonding connection accessible? Is the impedance you measured right for the estimated length of the bonding conductor? Does the pipe work test out as an extraneous part? Did you disconnect all parallel paths before testing?

Theirs no specified max, just as low as possible!!

I've had one install where the put s plastic fitting after the incoming water pipe
 
Theirs no specified max, just as low as possible!!

I've had one install where the put s plastic fitting after the incoming water pipe

I never said there was, but it's easy enough to work out roughly what it should be for estimated length of the bonding conductor.

What has the plastic fitting got to do with it?
 
I think this is a good question. What is a good figure? This question has been asked before and the answer is their isn't a given figure. I don't see how you can 'estimate' a length for the bonding if you can't find the incoming water supply. If you can then that's a different matter and you could then estimate from the known resistance figures for a 10mm conductor. But if you could see where it enters the house in order to make an estimate then you'd be able to test to see anyway if adequately bonded by using the 0.05ohms suggestion in GN8 (measuring between known earth and pipe), so I'm guessing Jo can't find where it comes in?

If you can't find the stopcock or where the water enters the house and can't find the bonding, then I would put it down as further investigation required as its a pretty important aspect to put down as NV.
 
I think this is a good question. What is a good figure? This question has been asked before and the answer is their isn't a given figure. I don't see how you can 'estimate' a length for the bonding if you can't find the incoming water supply. If you can then that's a different matter and you could then estimate from the known resistance figures for a 10mm conductor. But if you could see where it enters the house in order to make an estimate then you'd be able to test to see anyway if adequately bonded by using the 0.05ohms suggestion in GN8 (measuring between known earth and pipe), so I'm guessing Jo can't find where it comes in?

If you can't find the stopcock or where the water enters the house and can't find the bonding, then I would put it down as further investigation required as its a pretty important aspect to put down as NV.

You can have a pretty good idea of how long a cable would need to be to get from the CU to the furthest corner of a house and use that as a basis. Or just say that a 50m run would be around 0.1ohms so anything much more than that is likely to not be a main bond.
The 0.05 ohm suggestion in gn8 is between the bonding clamp terminal and the pipe being bonded, not between a known earth and a pipe.

You are right it's an important thing to not verify, and in a house there is very little excuse not to look for it. There's not that many different places where you can hide a stopcock in a house!
 
There's not that many different places where you can hide a stopcock in a house!

I wish you were 100% right there Dave!! I've had a right couple of pigs in the last five years..

A 25m long bonding conductor should be approx 0.08 for 6mm and 0.05 for 10mm....a 25m run would cover a lot of domestic properties quite easily. Get those leads zeroed!! And get past any oxidation on the pipework if you can't see the 951 clamp. 1.56 ohms on a 'normal' sized house sounds like a parallel path to me. I got 0.19 ohms through approx 4m of gas pipework recently. The existing main bond had been cut and pulled out of the wall when I was renewing it.
 
I wish you were 100% right there Dave!! I've had a right couple of pigs in the last five years..

A 25m long bonding conductor should be approx 0.08 for 6mm and 0.05 for 10mm....a 25m run would cover a lot of domestic properties quite easily. Get those leads zeroed!! And get past any oxidation on the pipework if you can't see the 951 clamp. 1.56 ohms on a 'normal' sized house sounds like a parallel path to me. I got 0.19 ohms through approx 4m of gas pipework recently. The existing main bond had been cut and pulled out of the wall when I was renewing it.

SNAP (post 8):yes:
 

Reply to Eicr in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. I have a small question about inspection interval labels. We all know to fit one of these labels with the relevant date upon completion of...
Replies
10
Views
750
Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
835
Had an enquiry where the installation (commercial) is relatively new and client has requested a condition report. Probably 80-100 circuits plus...
Replies
8
Views
1K
Looking for some advice and timescale here. I'm not an electrician just a tennet with a housing association. I've been offered top floor flat in a...
Replies
6
Views
458
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
781

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock