Hi guys just been to carry out an EICR on a TT system. Small flat and I came across the following: my question is is the cat codes valid I think. Now I have not done the cert yet and I'm between jobs so quickly wrote this so don't bite my head off for not using the correct terminology or using the correct sections within the cert!
Unable to locate stopcock to confirm earth connection C2
Ip rating under consumer unit C2
Hole in patress box C3
Inner cores of T+E visible outside enclosure c3
Unsupported cables C3
Ring main - earth continuity high 6.06 ohms C3? Or C2 my end to end readings for E and L were 0.55
cheers guys appreciated as ever!