Ive got my assessment with elecsa soon and im hoping someone can help me out with a few questions, the senario i have is:

A Garden shed which is fedd from a ring main in the house, spured off into a un sw fused spur, then from there 2.5 armoured cable in to a metal clad RCD fuseboard in the shed, there is a lighting circuit and 2 sockets on a radial in the shed.

what i am wondering is how do i do the EIC for this instalation as i am unsure about it and really want to get it spot on for the assessment.

Thanks in advance i really hope someone can help me out

regards
Lucus
 
would you test the ring main on one schedule off test results incuding the submain supply, and then have a seperate schedule off test results for the shed C/U?

thanks for your help
 
one question. is the ring main in the house RCD protected. if so, you then have 2 RCDs on the shed circuit, presumably with no discrimination. a fault in the shed could take out the house ring main.
 
Last edited:
hi

yes there is 2 rcd's with no descrimination would this be a problem for the assessment?
also is the cable too small? if its protected why is it a problem?

regards
 
Last edited by a moderator:
To be honest Lucus this is perhaps not the greatest install to show on an assement, the very fact that you have no discrimination becasue of using a spur off the ring final circuit proves bad design.

As you had used SWA you had no need to RCD protect it going out to the shed. So it could have either come of the unprotected side of the CU if you had one or you could have henly blocked the tails and fitted a small single board or a shower enclosure type board.

Also fitting a small board of a ring final via a FCU be it unswitched or not, is not a good design. You could have spurred direct off the ring final to the Shed into again a single enclosure with a 16amp protection device then to your sockets and then a FCU for the light, with a 3amp fuse.

As this is a shed what earthing supply have you? if it is TNC-S then did you get permission from the DNO to export the earth.

The size of the cable will depend on the run, as you have backed the cable with a 13 amp cartridge fuse. How far is the shed and did you do the calcs for load and volt drop.
 
thanks for your reply, this is in my own house which is the only reason i put a cu in the shed as it didt cost me alot, would you recommend that i run a seperate 2.5 twin from the main cu and put it on a 20a mcb and connect this to the armoured, then remove the rcd in the shed cu and put a main switch in its place, then use a 16amp mcb for the socket radial and keep the lights on a 6amp, as for the earth im using the tncs earth is there a requirement to ask them ive not heard about this before, would i be better to use a earth rod instead?

thanks for your help everyone its greatly appreciated.

lucus
 
this install could catch you out, if i was you, try to find something else, as you have seen by the replies, you may have difficulties.
 
do you think i would still have problems even if i put it on its own feed direct from the house fuseboard on a 20a mcb and disconected from the fcu?
 
hi everyone
not long now until my assessment with elecsa, i have changed this instalation now, it is as follows:
20a mcb in house consumer unit rcd protected, 2.5 twin and earth to external enclosure, 2.5 armoured to a 2 way consumer unit, and from there there is a socket radial feeding 2 double sockets on a 16amp mcb and lighting on a 6amp mcb, so i have discrimination for fault protection, i have a rcd in the 2 way mains at present but am not sure if i should change this to a main switch so its only protected by the house rcd, as i wont have any discrimination with 2 rcd's.

any advice would be greatly appreciated

cheers
 
easiet way is to replace the shed rcd with 2 pole isolator, but, is there any way you could feed from non-rcd section of the house CU?
 
the house cu is a small single rcd board it doesnt have a non rcd option, also the twin and earth comes down the corner of the inside wall so would need rcd protection anyway.
cheers
 
the ideal situation would be to replace the existing CU with a new board. RCBOs for the house. 20A MCB for the shed. RCD and 2 MCBs in the shed. As you say, its a small board, so cost would not be excessive, and you would have made a major improvment to the house installation, and have a job to be proud of for assessment.
 
Last edited:
Change the CU and use this as your assessement,if it is your first which I think it is, concentrate only on the CU change in your house.(You only need one job on 1st well I did unless it has changed)

The assessor is not there to test your design skills but to make sure you are SAFE and COMPETENT to carry out electrical work.

He or She will ask you to demonstate basic testing procedure ie PFC ZE or RCD trip times or even continuity of protective bonding conductors along with asking questions re knowledge of the BRB.(Basic)

They will look at you EIC & both schedules to make sure you are testing correctley and recording correctley.

You will find that the assessor is only human and they were in the same position at some time in their carreer and will know that you are apprehensive and uneasy.


The info from the forum members is spot on and that what this forum is all about.(IMO).



Good luck and post how you get on.
 
hi
surely the shed feed would still need rcd protection from the board as the cable is a normal pvc twin and earth conceled within the wall down a corner, it is less than 50mm can someone correct me if im wrong

cheers everyone for the help.
 

Reply to Elecsa assessment soon questions about EIC for job in the Certification NICEIC, NAPIT, Stroma, BECSA Forum area at ElectriciansForums.net

Similar Threads

A bit of a mini essay but these questions have been building up in my mind over the last weeks and months as I've been studying and volunteering...
Replies
6
Views
3K
Hi. I thought I would introduce myself on here in the hope to gain some valuable information on setting out on my own. I'm 42 and have been an...
Replies
116
Views
10K
Stroma Certification Scheme Stroma Assessment questions
Hi Everyone, I have my first Stroma assessment coming up, i qualified from college a few years ago and have been working building up my...
Replies
16
Views
7K
Hi guys I'm a recently qualified C&G Level 2. I have my 18th edition on the way in the next few weeks. I have a CCNSG AND IPAF 3a/b card, happy...
Replies
0
Views
967
Stroma Certification Scheme Stroma Assessment - Speedy and Proper
hi all I've been reading a few posts about stroma I can only speak of my expereance so here goes After carefull deliberation I chose stroma (£288...
Replies
5
Views
3K
hightower
H

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock