This brings another problem to the fray which is my chosen CU only has 40 or 50amp MCBs. I know there is no requirement to provide overload protection for fixed loads but then my breaker is lower than my design current at 40amp and 50amp is above the 47amp allowed by the cable?

Alternative is to use an MK Sentry CU which has the 45amp breaker option
 
The 9.5kW shower is perhaps only 9.5kW at 240V, taking just under 40A. At 230V it will be a lower output? If you use a 40A MCB, I'd be surprised if it tripped.
 
Either take SJD's suggestion 9.5kW @ 240V is 38A at 230V so a 40A breaker is fine.
or use an MK / Schneider CU to use a 45A MCB
Or as a shower is designed as short term load with no variation and a 40A MCB will take 41.3A for in excess of 2 hours this will not trip and cause nuisance.
The cable is protected as it can take 47A, you have short circuit protection and you are not designing a circuit where a small overload of long duration will occur. You are designing a small overload of short duration; this is permissible in the regulations, as other wise diversity calculations would not be possible. Although no diversity is permitted for showers this is a design decision that is safe and in accordance with common practice .

OK so write that down and have it available just in case the assessor should ask about your design calculations, (they very likely won't, unless they are reading this post!)
 
The assessors I have met are looking to pass you. You just have to make it easy for them. Make sure you have all the items on the assessment check list sorted and available. If you do not know the answer to a question do not try to bluff, just say you don't know and say where you will look it up, usually the On Site Guide. None of us, well perhaps the odd one, can remember everything.


Good luck.
 
No it wasn't at all, in a strange way I actually enjoyed it once we got going, was a chance to exercise the old grey matter and even bounce a few questions off the assessor to get their take on things.

The assesor actually said himself he would have put the wire in question in trunking for the 6 inch run above the CU - it looks a c*ck clipped to wall (it is in pantry but just not a massive fan of bare T&E). He was pleased that I had considered the consequences of this with regard to CCC all the same so I guess they aren't trying to trip you up and if you can back up what you are doing then you have nothing to worry about.

I guess just nerves took over, all the mentions of "assessment" and the huge sums of money involved.
 

Reply to Elecsa Part P Scheme - Testing Queries in the Certification NICEIC, NAPIT, Stroma, BECSA Forum area at ElectriciansForums.net

Similar Threads

NICEIC Certification Scheme Getting accredited to
Looking for some advice regarding joining a CPS. I've been in the electrical industry in various roles for nearly 10 years. I started my...
Replies
15
Views
836
Hi, I had been with Elecsa for years as a Part P installer/tester. Then they were taken over by the NICEIC. I'm embarrassed to say that I hate...
Replies
6
Views
1K
Hi all, I am going to fully rewire my house. What do I HAVE to do once I’ve rewired it? I am an approved spark, but do not have part P. Do I need...
Replies
11
Views
2K
Completed my AM2s start of this year. My whole career plan is to run my own company/sole trader. Be my own boss basically. I always get asked...
Replies
14
Views
670
Hi, as I’m trying to grow my little business I keep coming across many obstacles namely trying to join a competent trade scheme. NAPIT seem to be...
Replies
92
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock