As there are so many “different ways to skin a cat” in our industry, I thought I would post the below to see if anyone has anything they would like to share on a job I have coming up
60m2 ish of electric under floor heating split into 3 zones and also on 3 stats (stats can only switch a max of 16a unless you install contactors etc) zone 1 is kitchen, Zone 2 is hallway and zone 3 is bathroom total loading around 9kw / 37a
I am thinking it’s probably best to run a separate radial for both kitchen and hallway from the CU given the fact these are the largest areas and can probably only fit 2.5mm into back of stats etc and then probably pinch a feed from the ring via an FCU for the bathroom
Like I said, there are many different ways to do it but just thought I’d throw up a post whilst I was online. Haven’t really given the job much thought as yet.
Cheers