I'm just looking for opinions here on my uncle's farm. He had several new large outbuildings erected within the past three years. At the source, the sparky fitted an 80A 30mA RCD as the main isolator which protects all the other outbuildings at one part of their farm.

From here, they take a supply from an mcb to another building which has an enclosure with a 100A 2-pole isolator. This shed then has a supply taken from it to another outbuilding. i.e A-B, B-C,C-D.

The problem here, is the 30mA RCD. If damp etc gets into a light or switch, the other lot goes down and their well pump goes out to and thats a big problem during frosty weather cause if the power is off, the pump will freeze.

The sparky that did the job is now working in China but I asked another sparky who was doing work at a factory I was visiting and he said their isn't much that can be done as it has to be on a 30mA RCD since its TT.

I have a good enough knowledge of understanding electrical work but there are areas I am not clued up on. Cheers
 
I'm just looking for opinions here on my uncle's farm. He had several new large outbuildings erected within the past three years. At the source, the sparky fitted an 80A 30mA RCD as the main isolator which protects all the other outbuildings at one part of their farm.

From here, they take a supply from an mcb to another building which has an enclosure with a 100A 2-pole isolator. This shed then has a supply taken from it to another outbuilding. i.e A-B, B-C,C-D.

The problem here, is the 30mA RCD. If damp etc gets into a light or switch, the other lot goes down and their well pump goes out to and thats a big problem during frosty weather cause if the power is off, the pump will freeze.

The sparky that did the job is now working in China but I asked another sparky who was doing work at a factory I was visiting and he said their isn't much that can be done as it has to be on a 30mA RCD since its TT.

I have a good enough knowledge of understanding electrical work but there are areas I am not clued up on. Cheers
That damn E54! :D You could put a time delayed 100mA upfront ,then submain before the 30mA rcd, then do the same at each of the other sheds with each having its own earth stake, good 5/8" rods coupled together would be best and link them all together, that shoud give you a decent Ra
 
In other words, your saying to fit a 30mA RCD in each enclosure with the 100A Isolator. Like a split board with the 100A Isolator and mcb for supply to other shed, on one half and the 30mA RCD on the other half with that sheds circuits protected by it?

By linking the rods, I take it the armour/cpc of the swa between the sheds is the 'link'?
 
In other words, your saying to fit a 30mA RCD in each enclosure with the 100A Isolator. Like a split board with the 100A Isolator and mcb for supply to other shed, on one half and the 30mA RCD on the other half with that sheds circuits protected by it?

By linking the rods, I take it the armour/cpc of the swa between the sheds is the 'link'?
Yep all sounds good to me
 
Yes i agree with that, but why can't people do it properly in the first place...... stupid question I know the answer to that.
 
I wasn't finished yet and was still open to opinions from other people. On another electrial forum, a few sparks there have stated not to use a 100mA RCD but a 300mA S Type instead. I mentioned the earth rod at each shed to help with the Ra and they joked.

No point thanking you now after 'your' insult. btw, I am doing this between flights so my responses will be delayed.
 
I wasn't finished yet and was still open to opinions from other people. On another electrial forum, a few sparks there have stated not to use a 100mA RCD but a 300mA S Type instead. I mentioned the earth rod at each shed to help with the Ra and they joked.

No point thanking you now after 'your' insult. btw, I am doing this between flights so my responses will be delayed.
Well why don't you just read the regs book and determine for yourself what it needs instead going from forum to forum getting different peoples opinions! but i know what i would do, i assume your not an electrician though
 
Let's get one thing clear straight away, ...it wasn't ME!! lol!!

Frankly, from what i can make of this installation, it's a mess, and has been designed and installed by someone that really hasn't a bloody clue!! One 30mA RCD to protect several buildings circuits on a farms TT system, ...Jesus!! And what happens if that single device ever fails?? lol!!

It doesn't matter much whether you use a 100mA or 300mA up front S type RCD, probably in this case better to utilise a 300mA if the the source supply is feeding several buildings. The problem then comes from discrimination between the buildings!! It would have been better to of had 2 DB's at source, one to supply the sub-mains to these other outbuildings and the other to supply the final circuits installation within the source building.


Anyway it seems that each supply is piggy backed off the DB's in other out buildings, which is going to make things very difficult unless you split these supply sub-main cables away from the individual outbuildings final circuit DB installation (which should all be provided, with 30mA protection), leaving the sub-main cables protected only by the 300mA source RCD, (final distribution circuits will have both 30mA and the 300mA back-up protection)


Earthing wise, there should be at least one deep driven earth electrode position at each of these outbuildings, connected to the EMT of each building, which should in turn be linked together preferably by a 3rd core in the SWA sub main cables, or via the armours. If these outbuildings are steel constructions, even better (depending on construction method) but first check if the steelwork is providing a decent Ra value and if so, link it with any made deep driven electrode position.


Basically without going in to too much depth, (not feeling too great today lol!!) the outbuildings 30mA final circuit protection should not be in series with the other upstream buildings.
 
@derek I don't know the Ra but will have to find out.

@Engineer54 Many thanks for the detailed reply. The sheds (all are 100ft or more long) are all steel girder constructed with the post/trusses in each shed joined like one big steel frame.
 
@derek I don't know the Ra but will have to find out.

@Engineer54 Many thanks for the detailed reply. The sheds (all are 100ft or more long) are all steel girder constructed with the post/trusses in each shed joined like one big steel frame.

It depends more on whether the posts have been driven into the ground, or concreted into the ground, as to whether they will provide an additional earthing facility (even better if a steel re-bar mesh has been laid in the floor slab).

Whether they do or not, at the very least they will almost certainly be earthy, (extraneous earth) so these steel framed buildings will need to be bonded anyway, to the buildings MET/EMT positions!!

It will be interesting to know what sort of Ra we are talking about, on this existing installation??
 
Last edited by a moderator:

Reply to Electrical Setup in Farm Outbuildings in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I am asking on behalf of a friend who has an outbuilding that he uses as an art studio, the building is fully insulated and is currently heated by...
Replies
1
Views
531
Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
Replies
9
Views
507
Just thoughts Id share my recent fun and games on my parents farm.. The electrics are old. Its a 400yr old house with outbuildings just as old...
Replies
9
Views
1K
We are in the process of renovating our house, and would like to setup led strip-lighting throughout. of the options, this seems most attractive...
Replies
4
Views
721
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
837

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock