Hi,
I got 8 normally closed emergency stop buttons wired in series and 100 amp 4 pole contactor with 230v coils for the stop circuit. They require a key switch at the D/B to reset the circuit if a emergency stop has been hit and and after it has been twisted to reset the stop button, was just looking for ideas on type of key switch and how to integrate it in to the circuit.
 
Walk away from this.

This is an outdated design and does not comply with any current statutory regulations surrounding emergency stops.

An judging from the level of this question, and not knowing your background. I would say you aren't through any fault of your own competed to undertake this work.
 
You will need to do a risk assessment firstly to establish the level of safety system required.
Then you need to design the circuit based on this assessment, this may mean a dual channel e-stops and maybe even dual contactors in series with feedback from the contactors back into the safety circuit so if one of the contactors fails (welds closed) the circuit will not reset.
You will need a safety relay (Pilz or similar).
There is some good free software that you can use called Sistema that will help establish the performance level (Pl) for the system. Pl levels range from a to e with a being the lowest level.
The keyswitch will be wired into the reset circuit of the Pilz relay.
Hope this is of help, but be careful, safety circuits can be very onerous.
 
Walk away from this.

This is an outdated design and does not comply with any current statutory regulations surrounding emergency stops.

An judging from the level of this question, and not knowing your background. I would say you aren't through any fault of your own competed to undertake this work.
 
@Pete999 I thought you might have hit rob with he spelling emoji
 
@Pete999 I thought you might have hit rob with he spelling emoji
I'll only do that when it's blatant, not to Rob, mind you, you just made a spelling mistake by spelling Rob with a lower case letter.:D:p:rolleyes: Think I may have made a rod for my own back here still never mind eh.
 
3 station push button enclosure with stop start and momentary (spring return) key switch at panel (so key needs to turned and the start button pressed at same time) Wire the emergency stops in series with the stop N/C and start N/O and key switch N/O at the panel, with the hold in from contactor wired over the start and key switch.
 
Last edited:
3 station push button enclosure with stop start and momentary (spring return) key switch at panel (so key needs to turned and the start button pressed at same time) Wire the emergency stops in series with the stop N/C and start N/O and key switch N/O at the panel, with the hold in from contactor wired over the start and key switch.

You really should know this Phil....

There is a bit more to it than that I'm afraid!
 
3 station push button enclosure with stop start and momentary (spring return) key switch at panel (so key needs to turned and the start button pressed at same time) Wire the emergency stops in series with the stop N/C and start N/O and key switch N/O at the panel, with the hold in from contactor wired over the start and key switch.

You really should know this Phil....

Without knowing where and what this system is been used for then you cannot offer a solution, also given that what you suggest your answer won't comply to statutory requirements even at the minimum level, the best suggestion for the OP has already been put forward and that is to leave well alone, it's simple to make a functional system for any electrician really but it takes alot of experience and knowledge to design one that complies and covers your --- if ever the unthinkable did happen.
 
It just happens I am familiar with the situation this will be installed in, it is a college environment, where the power D/B with 100 amp contactor supplying sockets outlets, 13 16 32A, gas valves ect are controlled via the emergency stops around the workshop.

Explain how it won't comply with statutory requirements, it is not a piece of machinery, I am aware that additional stops should not be run at 230v but it will all be in the same containment system and in steel conduit, therefor it cannot be at extra low voltage.
 
Last edited:
It just happens I am well aware of the situation this will be installed it, it is a college environment, where the power D/B with 100 amp contactor supplying sockets outlets, 13 16 32A, gas valves ect are controlled via the emergency stops around the workshop.

Explain how it won't comply with statutory requirements, it is not a peice of machinery, I am aware that additional stops should not be run at 230v but it will all be in the same containment system and in steel conduit, therefor it cannot be at extra low voltage.

There are accepted standards for basic design irrespective of the safety level required, a risk assessment will also include the consequences of component failure ie 'is it fail safe' and what measure have been undertaken or what extra components have been put into the design to give the required level of fail safety, you also mention using the Start button to do 2 functions, first as just a start then also as a reset if an E-stop is operated, this would not be a good design, you should incorporate a seperate device be it a key, button or similar to reset the system usually by a deliberate action, your reset should not energise the circuit at the same time, this must be by the use of another device again be it a P/B or K/S etc, even colour coding of indicator lamps, buttons etc have guidelines, if the red stop is on the same station as an E-stop then a red button would not be permitted, some of these points are not statutory but a written agreement and risk assessment with the customer must be drawn up say if the customer wanted a non standard button colour or indicator, this may be because of existing systems say on workshop machinery follow an older code, it reduces the chance of confusion if everything is the same.

Given the limited info I would as a basic have all the E-stop buttons as key release only, this way the students cannot mess about with the E-stops then quickly twist and release and then deny all knowledge, another way around this is to have an indicator system to identify the operated E-Stop...all this would be discussed on-site, I have seen so many poor designs when I worked through the schools and comments about this issues they have with them such as the one I just hi-lighted should be avoided in the design stage.

I also ask the question why you cannot change the voltage, you are allowed to run different voltages in the same containment as long as all cables are sufficiently insulated to that of the circuit and or controls of the highest voltage.

Yes I know it is not a machine but you have to consider what may be plugged in will be energised when power is restored so there is no real relaxing away from standards that cover machinery control, it is still a safety system and by the fact it is controlling power to gas valves, possible extraction fans etc it would fall within the realms of the standards required for machinery thus the system should be design to meet it as such, even if you don't actually fall under the BS60204, you will fall under other standards and given they are all derived from the same blueprint it would most likely follow the same basic design requirements, if you have any knowledge of the BS60204-1 you will see many standards are actually repeated in the BS7671 especially that of O/L protection of motors etc... you will find this overlapping of regulations very common across the many different areas of British Standards.
 
Last edited:

Reply to Emergency Stop circuit in the Commercial Electrical Advice area at ElectriciansForums.net

Similar threads

Fitted a lot of this sort of light recently, with all tests reporting back through central Dali controller(s).
2
Replies
15
Views
746
nicebutdim
N
Yes, probably overthinkig, thanks.
Replies
6
Views
527

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top