S

sparky200

A couple of questions that have bothered me since 17th came in which I would appreciate comment on.

Firstly if I replace a battenholder in a bathroom with an enclosed light fitting and and cross bond to nearest water pipe do I need to ensure that the lighting circuit is RCD protected.
Also if I install an low voltage fan with transformer and isolation outside bathroom but off the lighting circuit do I need to provide an RCD.

Many thanks

Sparky200
 
is the pipe already bonded then? does the light fitting have an earth already? in that case you dont need to "cross bond", or supplementary bond the pipe. if the pipe has no bonding, then either your main switch needs to be an RCD or you need to install some main and supplementary (see your regs).

That used to be a simple no, but now pretty much every circuit (with a FEW exceptions) should be RCD, I go off the premise that if I'm not sure, bang one in.

Sorry I cant be more definitive.
 
If the fan isolator/transformerr are surface mounted external to the special location,the low voltage fan mounted in the special location No supp bonding or rcd required
The enclosed light replacing the baton holder it is replacement work only if it is still a class 2 fitting,again no req to rcd the lights
 
Isn't it the case that - apart from maintenance such as replacing the light fitting - you shouldn't alter or extend a circuit unless it is 17th Ed compliant? ....

i.e., RCD protection a definite requirement for all circuits passing through a room containing bath or shower, and supp bonding the not required if the three conditions met (extraneous part continuity to MET confirmed, 30mA protection, and disconnection times met).

Or am I missing the point here? (Quite likely!)
 

Reply to Enclosed light fitting and extending circuit in a bathroom in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock