Hi guys, I'm having trouble deciphering some manufacturer's specifications / installation instructions for a three phase dual 32A outlet EV charger.

The model in question is the W22 wall mounted unit:
Screenshot_20180611-112248.jpg

I can see that there are 2x 30mA RCD's inside the unit mounted on DIN rail.

I'm unsure about the supply protective device to be used. One data sheet says 2x 40A TYPE D MCBs and the installation instructions say 80A supply.

Anyone fitted one of these before?
 

Attachments

  • Installation guide Posts and Wallmounts.pdf
    3 MB · Views: 7
  • Fastcharge-Wall-Mounted-Combined-2.pdf
    1.1 MB · Views: 3
2 x 40A outlets require a 80A supply. sssssimplesssss.

using a type D MCB would mean you'll need to select cable size, not only for 80A and acceptable VD, but also to have a low enough impedance , coupled with your Ze and/or Zdb to meet disconnection times
 
not got experience of chargemaster ev units... only installed evbox and rolec. with some you effectively treat it as a consumer unit, with each connection on its own rcd and mcb or rcbo. the cable supplying the ev charger sufficient for both connections.
on a different note there is no diversity allowed for ev chargers either and dont forget to tell the dno via uk power networks when you notify it aswell.
 
If the unit is rated up to or above 13.8kva it is a requirement to notify the DNO before installation. This is so they can map the installations and ensure their network can cope with the additional capacity.
 
The dnos are also regarding charging points as stores of energy. Each charged battery not being used potentially being called upon to feed the grid. In the not too distant future either
 

Reply to EV charger protective device in the Electric Vehicles Advice Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm looking into solutions for someone wanting potentially two ev chargers and wondered if anyone here has had experience with this. They...
Replies
3
Views
2K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hello, I have a EV charger that is reporting over voltage and is unable to charge. the charger will operate up to 253V The solar inverter reports...
Replies
6
Views
3K
Has anyone installed the Gen 3 Tesla EV charger. Is an RCD required at the supply as it says it has a type A one built into the unit. Also can...
Replies
4
Views
3K
Qualified electrician has installed Zappi car charger outside house. Grid incoming goes to DNO cutout then to SPD then to meter then to henley...
Replies
21
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock