Discuss EV chargers and RCD protection in the UK Electrical Forum area at ElectriciansForums.net

goasis

-
Esteemed
Reaction score
400
Hi all, just having a read through the regs and code of practice on car chargers. Where it stipulates the use of RCD's "for charging points" eg 722.531.3.1, is that referring specifically to the charge point it's self, ( and the fact that protection may be contained with the unit) rather than the circuit supplying it, which depending on installation, may not require RCD protection. I'm guessing it is, as the COP has a note 5.6.2, mentioning issues over selectivity between protective devices for the circuit, and prietive devices within charging equipment.
 
The RCD may be within the charger itself.

But - the supply cable may need RCD protection in itself ( <50mm in wall etc etc) - SWA wouldn't
Hi, thanks, yes that was my understanding, was on a course recently and the tutor wasn't particularly clear on the matter.
 
I wouldn't worry too much about selectivity between protective devices on a circuit feeding a single device.
The reason for selectivity is to minimise nuisance (and possible danger) if an upstream device switches off power to a group of circuits instead of a lower rated device switching off power to just the faulty sub circuit.
I the case of an EV charger, if a device detects a fault and disconnects the power, the only effect is that the EV stops charging, whether the device that turns off is upstream or local. No nuisance or danger to any other circuit.
 
I wouldn't worry too much about selectivity between protective devices on a circuit feeding a single device.
The reason for selectivity is to minimise nuisance (and possible danger) if an upstream device switches off power to a group of circuits instead of a lower rated device switching off power to just the faulty sub circuit.
I the case of an EV charger, if a device detects a fault and disconnects the power, the only effect is that the EV stops charging, whether the device that turns off is upstream or local. No nuisance or danger to any other circuit.
To be fair, the COP does say, in effect, not to worry about it if it can't be achieved
 
To be fair, the COP does say, in effect, not to worry about it if it can't be achieved
sometimes in it unavoidable, the circuit requires RCD protection at source, irrespective of what is in the charger. if the charger is the only circuit from the rcd/rcbo then there is no inconvenience in event of a fault, if anything its a fail safe and back up as its not unheard of for the built in RCM/RCDs on some devices to not operate.
 

Reply to EV chargers and RCD protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
So regulation 722.531.3.1 says RCD's shall disconnect all live conductors. Is this requirement met if the charger itself contains a DP RCD? As...
Replies
15
Views
4K
Afternoon everyone, I have a quick question about the Tesla Gen 3 Wall Charger? Does it require Type A 30MA RCD protection or not. Only because...
Replies
3
Views
1K
I am an NICEIC contractor but I have never installed an Electric vehicle charger. I have watched all of the relevant NICEIC webinars (The wire) on...
Replies
18
Views
911
Hi. Not sure if it's the right place to ask, so won't be upset if it gets removed. Apologies if the terminology (PEN/PME/etc) is used...
Replies
44
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock