I have been tasked with inspection of testing of our 2 vehicle charging points.
other than the standard ZS and rcd times , does anyone know what additional testing may need to be conducted?

also we have a TNC-S supply with an outside metal tap about 2.5 metres away from 1 of the chargers , is this a problem?

i know at least 1 of the chargers has PEN fault protection , does this require testing in any way?
 
TL;DR
Required periodic test? EVSE
Do you also have a copy of the Code of Practice for electric vehicle charging?
It will be difficult to properly test and inspect an EV chargepoint without the proper equipment and training.
 
The standard EICR form is not best suited - electraform do the best form in my view for this but its for install rather than periodic, so needs some alterations.
You need to test the circuit, confirm it has been installed in line with manufacturers instructions and the Code of Practice.
Unless familiar with the charger you will need to read the instructions.
The functional test, which is where a test adaptor is good as it simulates all the different charge states. Perks of having your own EV is that when testing other chargers you can basically get a free charger out of it!!

Does the charger with rest of install place too great a load on the supply capacity, phone or email dno and check they know about the charger, you would be amazed how many arent recorded.
earthing systems, rcds all this has to be considered.
I have attached a copy of the basic ev charger install certificate from electraform to give you some idea...

I have been known to spend a few hours testing and inspecting a couple of chargers, you check the origin of supply out to each charger, the earthing, load management, functional tests, connections inside, with all that current and heat its surprisingly common to find loose terminals. if over tightened they mas as well leave the connections loose if the ends aren't crimped as it becomes so thin, the wires burn out. Check the IP rating, You need to look at the earthing system, especially as a lot of people used the 'not reasonably practical' get out from the 17th ed to avoid fitting rods so a lot of chargers are on PME with no PEN fault or Rods.
 

Attachments

  • evdw-20220507160246.pdf
    123.1 KB · Views: 27

Reply to EVSE risk assessment in the Electric Vehicles Advice Forum area at ElectriciansForums.net

Similar Threads

Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
829
NICEIC Certification Scheme Getting accredited to
Looking for some advice regarding joining a CPS. I've been in the electrical industry in various roles for nearly 10 years. I started my...
Replies
15
Views
860
Just thought I'd share this quick sobering story that happened to me a couple of weekends ago.... Overhead 230v lighting festoon, LED golf ball...
Replies
5
Views
732
Hi. I have a UK customer that has an agricultural building that will have a Diesel TPN generator supplying a corn dryer electrical installation...
Replies
1
Views
1K
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
405

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock