Lekky1

-
Reaction score
16
Hi guys, I have been asked to fit a ring main in a utility room currently being built with a outside socket and a lighting circuit with 4 led lamps and a outdoor light, this much I am comfortable with.

My issue is with the max demand,
The current consumer unit is loaded to the max with 212amp of mcb's
With a 60amp cut out fuse

So if I do the math 212a -40a x0.4 +40a
Gives me a maximum diversity of 108.8amp

So I'm already nearly twice my max demand already before I've started adding my circuits.

It's a 2 bed small bungalow, this seems hugely over rated, I would like to get my 1st NIC assessment done on this so i want to cover all bases.

So any ideas would be gratefully received, my thoughts would include
1. Request DNO to upgrade to 100amp cut out which would still not meet the criteria,

2. Test and possible down grade any overrated mcb's, there is five circuits for sockets????

3. Full load test

4. Could I apply diversity to each circuit independently ?

Here is the C.U and cut out 20181129_175817.jpg 20181129_175822.jpg
 
Work out the max demand on what is used and connected instead.

If the sockets were arranged on one circuit instead of five would the actual use be less ? If there were 8 circuits would the actual use be more ?

How will downgrading the circuit breakers help the actual use of the installation ?
 
you have got no chance on that .can you not alter any of the circuits to make ring .

That was what I meant on option 2, I haven't seen inside the C.u yet but I can only imagine the majority are run separate in radials, it would possibly undertake some destruction to convert to ring circuits unless I was very lucky but could be a viable option
 
Average night with the lights on, TV going etc you'd be lucky if that hits 10 amps. Add another 40 maximum if the shower is running.
 
Listen to Andy mate,diversity is not just about that single calculation....for instance if 1 lighting circuit is 6a mcb but has 7-8 points at couple of watts (leds) you’re not realistically ever gonna reach 6a,even if you put 100w bulbs in......
You’ve also got 4 radial circuits totaling 72a with 5 sockets on...
 
That’s up to you mate,but bare in mind that you are the one that has to justify your decision and calcs should the worst happen.......engineering judgement my tutor used to call it....I think you’ll be pleasantly surprised if you clamp it though :)
 
I know it's just a small bungalow with the usual domestic appliances that would never even come close to the max demand of the value of mcb's , especially with the old couple that live there, so If I do clamp test and see and prove I have adequate room for movement , would I create space for new socket circuit or just run a sub main?
 
I know it's just a small bungalow with the usual domestic appliances that would never even come close to the max demand of the value of mcb's , especially with the old couple that live there, so If I do clamp test and see and prove I have adequate room for movement , would I create space for new socket circuit or just run a sub main?

You could alter the original circuits as long as you tested and provided certification.
Where would you be running a sub main from and to ?
 

Reply to Exceeded max demand questions in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
965
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
711
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
246
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock