Hi is there somewhere or some website that gives you expected real life test results, so for example if I go and do some tests on a shower circuit that has a 7.6kw shower on a 32A what you would perhaps say the R1+R2 should be.

Reason for asking when I was doing my course my tutor said you should expect to see say 1/4 to 1/2 ohm on a cooker radial circuit for example. I appreciate you need to do the calculations which I am trying to get my head around, buts i find its helpful to know what you should be seeing and if there were any tables giving you any estimates.

Thanks
 
It will always depend on the size and length of cable used have a look at the On Site Guide Appendix 9 which is page 166.

Hope that helps


Chris
 
I think your tutor needs a swift talking to. How can he say you should expect to see any kind of reading? Depends on cable size, length, so therefore size of installation, position of board relative to end of circuit, too many factors to even begin to put in an expected reading.

I could give you an average of what I found doing 175 housing association periodics, but that would prove nothing.
 
It will always depend on the size and length of cable used have a look at the On Site Guide Appendix 9 which is page 166.

Hope that helps
Chris

IET Guide page 166 is appendix G (Remedial Work, and Periodic Inspection), the UNiTE Guide only has 106 pages, which OSG are you referring too.
 
:mad: Whoops, but I do wonder what OSG acat was referring too, but probably re-written a dozen times by now, so not very relevant, when you are in a hole and you can't see over the top stop digging. :eek:
 

Reply to Expected test results in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
972
OLDBOY
O
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
583
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
812
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
I got a TEXT message (i dont know them and i cant find out who they are from the phone number) "Hi speaking from Indeed Are you available to give...
Replies
15
Views
846

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock