So on the test results (see pictures) it states TT system, earth rod, however from the picture of the supply it can be seen that there is a suppliers earth which looks like tncs to me.
 

Attachments

  • IMAG1380.jpg
    150.3 KB · Views: 213
  • IMAG1074.jpg
    62.2 KB · Views: 225
Maybe it's a bit of earth going into an earth block in the head but with no link present, looks like it's a DNO earth but maybe nothing connect? Just a thought?
 
It's possible that the earth has been connected to the head at some point in time after the original installation was carried out.

Is there anything in the installation which would mean that a PME earth connection cannot be used?

Is the rod actually there?
Does the rest of the certificate make sense?
 
I was thinking that maybe the DNO upgrade the supply after the original installation. Only thing I can think of. I suppose one way to find out is to do a ze test.
 
Update.... Got called out to same job as outside lights where causing the rcd, that covers the majority of the premises, to trip. Found lose neutrals in the lighting circuit which seems to be the cause as they have been fine for 2 days now. Anyway while I was there I carried out a Ze and got a result of 0.13ohms. I would therefore say that it is tncs system.
Now that that's been determined what would your thoughts be on doing away with the rcd covering the whole board and use individual rcds? So as when a fault develops the whole board won't trip off.
 
It's a commercial installation. Looks as if it was originally a TT system that has been upgraded to a tncs system which would make sense given the 0.13ohm Ze. This means I could use single pole rcbos as the neutral doesn't have to be disconnected if a fault develops on a tncs system. Whereas with a tt system both line and neutral have to be disconnected.
 
Update.... Got called out to same job as outside lights where causing the rcd, that covers the majority of the premises, to trip. Found lose neutrals in the lighting circuit which seems to be the cause as they have been fine for 2 days now. Anyway while I was there I carried out a Ze and got a result of 0.13ohms. I would therefore say that it is tncs system.
Now that that's been determined what would your thoughts be on doing away with the rcd covering the whole board and use individual rcds? So as when a fault develops the whole board won't trip off.

Were the readings the same with Ze & Zpn?
 
Well from the picture I'm sure you would agree that it looks like a tncs system. The measurement confirmed it. Yes both the same.
 
I also don't think it has to be a tncs because the reading is low. I carried out testing to confirm that it was a tncs system. Which I suspected from looking at it.
 

Reply to explain this..... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, As mentioned, I’ve got what looks like a TNCS system but CPC is coming via an earth rod???? Not tested TNCS system yet to see if earthing...
Replies
9
Views
604
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Might be a silly question, but can a tt supply come into a property via underground . This property in question, has no overhead cables...
Replies
22
Views
857
Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Replies
14
Views
972
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock