Hi
factory unit with 800 amp supply 95 mm main earth and 50 mm main bonds
portakabin has been delivered as a permanent addition
wired on 10 mm 3 core swa and 32 a commando plugs
there is a water supply and metal parts.

am I right in saying that it will need to be put on a stake as the main earth and bonds are so big.

Thanks mark
 
Not again . . . . . I see more arguments, and quoting of regulations that have yet to appear in the books I read :90:. It's probably sat on terra-firma anyway.

It's personal choice Mark,

Export PME with bonding conductors, or 'TT' it with RCD etc. Both have pro's, both have con's.

Regards

Billy
 
Sorry Mark I see where your coming from mate, your saying that your sizing your bonding conductor to the size of the neutral of the supplier, so as your bond is 50mm then the supply neutral must be 150mm+ and table 54.8

In your case though mate your Kabin is not a PME, as your not allowed a PME system inside your installation, so in all intent and purposes you have a PME that at origin as been converted into a TN-S inside the installation
 
Sorry Mark I see where your coming from mate, your saying that your sizing your bonding conductor to the size of the neutral of the supplier, so as your bond is 50mm then the supply neutral must be 150mm+ and table 54.8

In your case though mate your Kabin is not a PME, as your not allowed a PME system inside your installation, so in all intent and purposes you have a PME that at origin as been converted into a TN-S inside the installation


yep agree with 1st bit

not sure i follow what you mean on 2nd bit please can you clarify thanks
 
Look at the definition of a PME or TNC-S which is Terra (Earth) Neutral Combined- Separated.

Once beyond the main intake you have just a TN system. The earth and neutral are now separated inside the system, so any further installations inside the complex will be just a TN separated, not a combined
 
If your going to extend the equipotential zone out to the kabin then any services to this Kabin will have to bond back to the MET via your wiring.

So if your going to use a SWA then you could use a 3 core, the 3rd core will be your bonding conductor and tie this at the Kabin with the SWA at both ends.
 

Reply to Export pme to portakabin in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
504
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
494
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Some friends are setting up a metal workshop inside a shipping container, on site at a commercial building that rents out studios, workshop space...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock