Working on supplying three phase power to a new shed in a farmyard. Running armoured underground. I was going to connect the armour to the earth rod at the Main DB then use the armour at the other end in the new shed as the earth in the new shed, bonding all extraneous metalwork to it. Is this acceptable or do I have to use insulating gland at new shed end and new earth rod there? Some confusion, as all existing outlying building have no earth rods of their own, just rely on cable armour back to main earth rod.
 
as steve said. rod it at both ends. the more rods the better. bit of luck , if you use 5/8 screwed together rods, go deep, you might even make engineer54 happy.
 
he can have mine now. i've no further use for him.
 
Ha ha!! .... Just the use of ''Real'' earth rods will make me happy!! lol!!

Preferably, at least 2 of your 1.2 m rods coupled together for depth and stability. As for how deep i normally go down, ...well i haven't used anything other than 3.2m, 3/4'' rods for as far back as i can remember now, so i guess that would be the depth i'm happiest with...lol!!
 

Reply to Exporting Earth on TT system in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
496
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
483
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock