Need to supply a cable for a garage extension,

'Plumber' has proposed 2 x 10mm T+E in 100mm ducting along with a water pipe, with no CU at the garage.

This will eventually be marketed as an annex which will include but no limited to, 1 shower (power unspecified), 1 electric water heater, possible multiple mounted wall heaters, macifier, lights and 12 sockets. The client at this point in time will also be storing 18 motorbikes inside so it could be used as a work shed for tools etc.

Would a 16mm armoured or 25mm armoured run in the ducting instead of the 2x 10mm T+E with a CU in garage be a more suitable choice taking volt drop into consideration??
 
You will need to specify a little more information please.

DNO supply type and size.

Extraneous parts in the garage?

Length of sub-main run and installation methods?

Total loading in the main house building?

Total loading in the garage for what you are doing and expected expansion?

Why no CU in the garage surely this is a deffinite requirement?
 
TN-S
80A main fuse, 25mm
None
Installation Method D
40m run, Installation method in house B
Total load of entire installation expected to be within 80A

Is it a requirement? Presumably I would think so, with a separate earth electrode for the garage. Could you point me in the right direction of BS7671 so I can inform the client?

Appreciate the quick reply
 
Why don't you take a look through BS7671 yourself then come back to us with your findings. Then we can point you in the right direction..
 
Proposed works for next year, so can be part of one of the scams.

Can't find specific regulation regarding extensions apart from the obvious (do danger, to persons, property, livestock) and existing installation must meet requirements of additions and alterations.

I would design it incorporating 16mm or 25mm (depending on loading) two core armoured through the 100mm ducting feeding a sub-main CU, rather than the plumbers 2 x 10mm T&E. Bearing in mind a water pipe is travelling in the same duct.

Have been advised of use of Earth rods as this surpasses the event of a fault travelling from the garage through the house. Any exposed/extraneous conductive parts can use the Electrode.

Any help would be appreciated.
 
Its funny that I have seen this post on here,

I done a similar job as part of an install not to long ago,

we used a 10mm cable twin and earth (grey one) in ducting.

Simple, three letters FCU. Avoids any consumer units so no need to notify anyone

Simples!! Hope this helps
 
Its funny that I have seen this post on here,

I done a similar job as part of an install not to long ago,

we used a 10mm cable twin and earth (grey one) in ducting.

Simple, three letters FCU. Avoids any consumer units so no need to notify anyone

Simples!! Hope this helps

Me thinks that you should read the thread from the begining before making such statements and if you have read the thread from the begining STOP giving advice
 
Its funny that I have seen this post on here,

I done a similar job as part of an install not to long ago,

we used a 10mm cable twin and earth (grey one) in ducting.

Simple, three letters FCU. Avoids any consumer units so no need to notify anyone

Simples!! Hope this helps

If you have the regs you'll know that "showers" are notifiable - but I suspect you spend your money on feeding your horse.
 
Proposed works for next year, so can be part of one of the scams.

Can't find specific regulation regarding extensions apart from the obvious (do danger, to persons, property, livestock) and existing installation must meet requirements of additions and alterations.

I would design it incorporating 16mm or 25mm (depending on loading) two core armoured through the 100mm ducting feeding a sub-main CU, rather than the plumbers 2 x 10mm T&E. Bearing in mind a water pipe is travelling in the same duct.

Have been advised of use of Earth rods as this surpasses the event of a fault travelling from the garage through the house. Any exposed/extraneous conductive parts can use the Electrode.

Any help would be appreciated.

As Sintra says have a look at the BGB and list us your conclusions
 
Need to supply a cable for a garage extension,

'Plumber' has proposed 2 x 10mm T+E in 100mm ducting along with a water pipe, with no CU at the garage.

This will eventually be marketed as an annex which will include but no limited to, 1 shower (power unspecified), 1 electric water heater, possible multiple mounted wall heaters, macifier, lights and 12 sockets. The client at this point in time will also be storing 18 motorbikes inside so it could be used as a work shed for tools etc.

Would a 16mm armoured or 25mm armoured run in the ducting instead of the 2x 10mm T+E with a CU in garage be a more suitable choice taking volt drop into consideration??

Let the plumber do the job and sign it off. FFS!
 
Is there any advice (not FCUs everywhere!!) that may help me defeat a plumber who intends to use part p to take this work?

is there any justification in using 2x10mm cables instead of my proposed 16mm or 25mm cable?

Any help would be appreciated.
 
Its funny that I have seen this post on here,

I done a similar job as part of an install not to long ago,

we used a 10mm cable twin and earth (grey one) in ducting.

Simple, three letters FCU. Avoids any consumer units so no need to notify anyone

Simples!! Hope this helps

How does fitting a FCU make it non notifiable? Also I'd love to see that 10mm terminated into said FCU.
 
Is there any advice (not FCUs everywhere!!) that may help me defeat a plumber who intends to use part p to take this work?

is there any justification in using 2x10mm cables instead of my proposed 16mm or 25mm cable?

Any help would be appreciated.
Err, remind the PLUMBER its an ELECTRICAL job and he should restrict himself to unblocking toilets?
 

Reply to Exporting Supply To Garage Extension, Cable Sizing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
614
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
546
Hi guys, Can I ask you a DIY question? I'm refurbing a detached garage and adding a garden building. Garage currently has a submain supplied by...
Replies
1
Views
797
I'm converting my old garage into a two bedroom annex. At its nearest point it is approx 10m from main house. I plan it to be all electric, UFH...
Replies
5
Views
3K
I have had a kitchen extesion built on an old property (c.1810), which has an unusual consumer unit situation. Part of the property has only a...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock