Hi, I am new to this forum and can't find an exact match to my search.
I am new to testing and inspection and have come across a db mounted in a garage on the wall whereby the t and e's for all circuits are clipped direct to the wall before entering the ceiling approx 1m above.
Is this deemed as a C2 or C3 on test cert?

Thanks.
 
Advertisement - Content continues below

Spoon

-
Mentor
Arms
Esteemed
What is wrong with having cables clipped to a wall?
 
Last edited by a moderator:

Andy78

-
Mentor
Arms
Esteemed
The cable's sheath is sufficient to protect the basic insulation. What's the issue you perceive and which regulations do you think this is against ?
 

Spoon

-
Mentor
Arms
Esteemed
Its even mentioned in Table 4D5, Reference Method C. (Clipped Direct)
 

Spoon

-
Mentor
Arms
Esteemed
Oh, and welcome to the forum mate.
 
  • Thread Starter Thread Starter
  • #8
Thanks all. My thinking is with reference to the condition report section 4.16 where the cables are not mechanically protected.

IMG-20190423-WA0010.jpg
 

Strima

-
Arms
Esteemed
I have to ask, what’s your electrical experience and qualifications?
 

Andy78

-
Mentor
Arms
Esteemed
Thanks all. My thinking is with reference to the condition report section 4.16 where the cables are not mechanically protected.
What do the regulations referenced in section 4.16 have to say about the example of wiring you are inspecting ?
 
N

Nigel

The outer sheath is classed as mechanical protection. The environment the cables are installed in will dictate if it is sufficient mechanical protection. For example T&E clipped on a wall at high level with nothing around it would not warrant any code. T&E clipped just above a shelf used for heavy items may warrant a C2/3.
 
  • Thread Starter Thread Starter
  • #12
What do the regulations referenced in section 4.16 have to say about the example of wiring you are inspecting ?
Hi Andy. Thanks for your help on this. Really appreciated. I have re-read the sections in the regs and they refer to mechanical strain, not mechanical protection as I had read it earlier too hastily.
 
Last edited by a moderator:
  • Thread Starter Thread Starter
  • #13
The outer sheath is classed as mechanical protection. The environment the cables are installed in will dictate if it is sufficient mechanical protection. For example T&E clipped on a wall at high level with nothing around it would not warrant any code. T&E clipped just above a shelf used for heavy items may warrant a C2/3.
Thank you. I perceived the regs incorrectly.
 

Ian1981

-
Mentor
Arms
Esteemed
A code maybe deemed necessary if the top of the consumer units IP rating (IP4X) is compromised where the cables enter the enclosure
 

telectrix

-
Mentor
Arms
Esteemed
might not warrant a code, unfortunately there isn't a code for an eyesore. it's R.A.F. ( Rough As F*CK)
 
Electrical2Go - Online Electrical Supplier
This official sponsor may provide discounts for members
Advertisement - Content continues below

Reply to Exposed T and E's during test. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Aico Carbon Monoxide Detectors
This official sponsor may provide discounts for members
Advertisement - Content continues below
Top Bottom