Hi, I am new to this forum and can't find an exact match to my search.
I am new to testing and inspection and have come across a db mounted in a garage on the wall whereby the t and e's for all circuits are clipped direct to the wall before entering the ceiling approx 1m above.
Is this deemed as a C2 or C3 on test cert?

Thanks.
 
What do the regulations referenced in section 4.16 have to say about the example of wiring you are inspecting ?

Hi Andy. Thanks for your help on this. Really appreciated. I have re-read the sections in the regs and they refer to mechanical strain, not mechanical protection as I had read it earlier too hastily.
 
Last edited by a moderator:
The outer sheath is classed as mechanical protection. The environment the cables are installed in will dictate if it is sufficient mechanical protection. For example T&E clipped on a wall at high level with nothing around it would not warrant any code. T&E clipped just above a shelf used for heavy items may warrant a C2/3.

Thank you. I perceived the regs incorrectly.
 
A code maybe deemed necessary if the top of the consumer units IP rating (IP4X) is compromised where the cables enter the enclosure
 
might not warrant a code, unfortunately there isn't a code for an eyesore. it's R.A.F. ( Rough As F*CK)
 
On an older existing installs I am not overly fussed about clipped direct so long as it shows no evidence of damage.
I have clipped twin and earth in my garage from new been there for 30+ years and absolutely fine with this.
Same with older installs with non rcd on the lighting I am not overly concerned.
I have non rcd lighting.

Now if in the OP the cable sheathing was all chaffed and bashed up I would suggest so over capping
 

Reply to Exposed T and E's during test. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Afternoon everyone.. During some testing I have found an IR reading of 0.01MΩ between N-E. This is on a length of SWA buried underground from the...
Replies
17
Views
3K
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
480
I have a TPN board that will feed 8-10 sub boards. The loads on each board are negligible 5-10 amps peak but mostly 1-2 amps. The distribution...
Replies
26
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, First post here, hope I'm compliant with the rules! I did do a quick search before asking this, but I couldn't quite come up with the...
Replies
3
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock