Octopus

As the title says. Customer wants 2 extra sockets added in their kitchen and there is a redundant cooker point "available" on a 32A breaker.

Using 2.5mm T & E to add the extra sockets, I'd drop the breaker to a 20A MCB but a mate says no leave it as a 32A.

The extra cable run is 3 or 4 metres.

Over to you good people!
 
It's no different to spurring off a ring really. Use 4MM cable and keep the 32A MCB or 2.5MM and drop it to a 20A MCB.

Or if you're not doing it tell your mate to use 6MM and have a laugh when he tries to connect 2 6MM cables at the back of the socket.:goofy:
 
It's no different to spurring off a ring really. Use 4MM cable and keep the 32A MCB or 2.5MM and drop it to a 20A MCB.

Or if you're not doing it tell your mate to use 6MM and have a laugh when he tries to connect 2 6MM cables at the back of the socket.:goofy:

He wants 2 extra sockets, spurring off a ring would only be one socket.

Drop the MCB to 20A...
 
Just do a lollipop ring, in 2 1/2 mil,saves sizing down on the breaker.
Trouble with that, you'll have a ring with a radial, For testing R1 + R2 you'll be cross connecting the ring part at one of the sockets and then you would have to test at the other socket, then test at the breaker for R1 + R2. And then make sure it all complies LOL

A
 
As it's only a couple of sockets, treat it as a radial, and size the MCB to the lowest rated cable.
If using 2.5mm² 20A, if 4mm² 32A.
If there were to be lots of extra sockets, then I'd go for the lolipop in 2.5mm².
 
Depends what the sockets are for, but quickest most bombproof way would be extend as 4mm rad and leave the 32A breaker in place.
BTW 2.5mm in pucker conditions carries, tops 27.5A
 
Somewhere in the deep recess of my mind i thought you had to keep the same size cable all along its length, can't remember for the life of me. Any one else know?
 
Id say you can leave it on a 32A breaker as long as you making them two sockets into a ring. (which would be a complete waste of time). So yea 20A breaker I'd go with. Only advantage of making it a ring is that you could actually spur off if you wanted any extra sockets in future.
 
Id say you can leave it on a 32A breaker as long as you making them two sockets into a ring. (which would be a complete waste of time). So yea 20A breaker I'd go with. Only advantage of making it a ring is that you could actually spur off if you wanted any extra sockets in future.

Why is there a problem spurring of a radial? You are just extending the radial.... ;)
 
Cheapest way: Use 1mm T&E and keep the 32 MCB....
Or wet string... but make sure you take cash there and then cos its not so good when it dries out.
 
As the title says. Customer wants 2 extra sockets added in their kitchen and there is a redundant cooker point "available" on a 32A breaker.

Using 2.5mm T & E to add the extra sockets, I'd drop the breaker to a 20A MCB but a mate says no leave it as a 32A.

The extra cable run is 3 or 4 metres.

Over to you good people!

Sorry to sound dense here Murdoch, but who's job is this, yours or your mates?
 

Reply to Extending a 6mm cooker point in 2.5 T & E in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
512
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
595
Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...
Replies
14
Views
756
The ongoing kitchen refit..... I have chased and fitted 10mm T&E from the cooker outlet to the isolator switch and up into the loft. I have 4...
Replies
4
Views
1K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock