Hi have just extended a ring main,am i correct in thinking that i have to test the complete circuit and give customer an e.i.c or do i issue a minor works and just test the extended circuit ?
 
you have to test the whole circuit that you have altered, not the whole installation.a minor works cert will de OK as you have not installed a new circuit. on a MWC you will see it asks for the "details of the modified circuit"
 
If by extending you mean that the ring is now longer IMHO its a EIC as you need to test the entire circuit.

If you've added a spur you could use a MWC and restrict your tests to the spur.

tin hat on
 
Thanks guys,what i have done is actually opened up the ring and added 4 doubles so to be on the safe side test the ring completly and issue an EIC p.s murdoch IMHO ??
 
Hi Murdoch, fix bayonets :)

Agree with Tel, not a new curcuit. Ok, a slightly more complicated than a radial, but it still existed prior too. Now with a bit tacked on? Why EIC?
 
Yh minor works certificate, check bonding and test that circuit. 1 minor works certificate for each alteration, thats why if uve altered a couple of circuits then you use a EIC saves writing out numerous minor works
 
Minor works if your alteration or addition is to one existing circuit only...no matter how extensive the alteration.
The only thing with a M/W is there is no provision for recording end to end ring readings...you should still test these,and the results could be recorded in the comments on the existing box.
 
Minor works if your alteration or addition is to one existing circuit only...no matter how extensive the alteration.
The only thing with a M/W is there is no provision for recording end to end ring readings...you should still test these,and the results could be recorded in the comments on the existing box.

Hence why I would use an EIC
 
Minor works if your alteration or addition is to one existing circuit only...no matter how extensive the alteration.
The only thing with a M/W is there is no provision for recording end to end ring readings...you should still test these,and the results could be recorded in the comments on the existing box.
there is on the certs i use.
 

Reply to extending ring main in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
811
Hi guys I am looking to add 4 additional sockets for a room that is being converted for a bed ridden person. The room at present has no sockets in...
Replies
7
Views
1K
Hi all I would like to put some sockets in the attic and keep them on the main house ring main. Am I right in saying I can pull one of the legs...
Replies
1
Views
179
Evening all, I just wanted to see if electrical improvers/adult trainees with appropriate levels of experience and who hold testing...
Replies
0
Views
1K
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
467

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock