Hello all

I'm to add an external flood light with pir with a switch indoors to turn on & off I have a RCBO consumer unit
Question is ....
1 - do I come of the lighting circuit into a swith then out to junction box to feed the light
Or
2 - I have a fused spur, shall I come of this into the switch then the outside light

Spur or lighting circuit?
Cheers
 
I presume this is something like a 50W or so LED floodlamp, and not a old 1kW halogen lamp that would likely trip a lights MCB/RCBO on switch-on?

Then both a 6A RCBO for lights, or a 3A/5A FCU off a RCBO protected circuit, are reasonable options. I personally would prefer coming off the lights supply simply as anyone in the future would expect a light to be powered from the circuit marked "lights".
 
I presume this is something like a 50W or so LED floodlamp, and not a old 1kW halogen lamp that would likely trip a lights MCB/RCBO on switch-on?

Then both a 6A RCBO for lights, or a 3A/5A FCU off a RCBO protected circuit, are reasonable options. I personally would prefer coming off the lights supply simply as anyone in the future would expect a light to be powered from the circuit marked "lights".
Definitely a LED its 50w ... guess it would make sense of the lighting circuit as there would be a switch in the living room for the outside light..... thanks
 
Double pole switching is attractive in terms of isolating any faults (including N-E from cable damage, etc), that could also be a simple DP switch off the lights supply.
 
i'd prefer a D/P FCU so as to be able to isolate it when it fills up with waterand trips your RCBO.
So come of the FCU rather than the lighting circuit? Then into a switch, I'll be connecting the light so the sensor can be bypassed & turned from inside when we want it on & when off the sensor will be back in operation
 
Yes, that looks fine.

Just make sure the light circuit is properly earthed and the CPC (earth wire) is attached to the plate.
Appreciate the advice, I'm going to feed of the lighting point in the living room into this switch, outside into a JB & wire the flood into this ... thats my plan
 
Appreciate the advice, I'm going to feed of the lighting point in the living room into this switch, outside into a JB & wire the flood into this ... thats my plan
Sounds reasonable.

For cabling outside don't use exposed T&E as it is not UV resistant (often it lasts years if north-facing so not direct sunlight but still bad practice). You can cover it in UV-tolerant plastic conduit as one solution, or use a UV resistant cable such as H07RN-F:
However, H07RN-F is very flexible so needs lots of clips to hold it straight if that matters to you!
NYY-J is another good choice for outdoor fixed wiring use, as it is much stiffer so tend to stay in place, for example:
It is a bit like armoured cable without the steel armour (so not OK for burial according to UK regs) and fine for places you don't expect severe mechanical threats.
 
Note the minimum bend radius for the likes of NYY-J and similar cables is usually around 12 times the diameter, so around the 12cm mark. That should be born in mind when thinking of taking cable out through a wall and then at 90 deg from there.

In that respect PVC conduit and junctions allow a neater sharper bend for using T&E (bent on flat side) if your route demands it.

Also you can get PVC conduit & accessories in white and black, so if white suites you decor better that might be another consideration.
 
Sounds reasonable.

For cabling outside don't use exposed T&E as it is not UV resistant (often it lasts years if north-facing so not direct sunlight but still bad practice). You can cover it in UV-tolerant plastic conduit as one solution, or use a UV resistant cable such as H07RN-F:
However, H07RN-F is very flexible so needs lots of clips to hold it straight if that matters to you!
NYY-J is another good choice for outdoor fixed wiring use, as it is much stiffer so tend to stay in place, for example:
It is a bit like armoured cable without the steel armour (so not OK for burial according to UK regs) and fine for places you don't expect severe mechanical threats.
I was going to use the NYYJ cable 1.5mm & wiska JB & glands make sure it's all IP rated, from the switch T&E out in the JB I'll make sure it's all earthed wouldn't want to risk a shock ....
 

Reply to External floodlight in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
487
Hello all, I know this is very simple but I would like some advice please. I am installing a new circuit to feed 5 external floodlights. It is...
Replies
7
Views
3K
Hi all, I have a log cabin in my garden. An electrician ran an armoured cable from my consumer unit to the log cabin and this terminates on the...
Replies
2
Views
623
Hi All, Would be grateful for some advice. Would like to add an additional light (Undercabinet 8W LED Batten light) to a two-way light switch...
Replies
7
Views
586
  • Article
Electrical2Go - Home Security: Using Floodlights, CCTV, and Door Entry Systems In an era where technology is advancing rapidly, home security has...
Replies
0
Views
205

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock