C

chrissyh

Just been reading through a recommendation to a client that advises that an external gas meter does not require bonding under current regulations. Can anyone confirm this?

thanks in anticipation
 
Havent heard that one within 600mm on consumers side still the norm. Is plastic piping with no exposed metal that might be the reason.

Hope someone can give you more precise details

Chris
 
external gas meters do require bonding on the consumers side,(the gas meter box is considered part of the building). generally if a meter is external you will find that the gas pipes are buried in the wall or screed inside the building. if you cant bond because of the plastic insert outside you have to bond on the first piece of available copper inside the building.within 600mm from the meter is preferable .

:)
 
Hi

Why would you want to bond an outside meter, you do not need to bond it unless its has a striking risk to a LPS system. You only need to bond inside of the property, if you can not achieve this you could bond at the meter but this is a none-preferred method
regards
 
Hi

nearly right, sparkswillfly its

Earth Bond to be connected to an incoming Gas Service within 600mm of point of entry to a premises. if practicable...

Regards
 
Hi


Not necessarily a lot of houses had meters put in sheds especially none parlour types, sorry to correct you but if we quote the regs we must get it right...


Regards
 
hi


I'm just trying to get to 100 posts I'm there

Thanks Sparkswillfly

Will I get a letter from the administrator or the Queen

Regards
 
Hi

Yea put your BS 951 clamp before pipe work branches off, we did forget that important bit....

Regards
 
Last edited by a moderator:

Reply to External gas meter in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, So my factory needs more power, currently 100A/3p (70KVA) => 400A/3p (200KVA) UKPN wont upgrade existing supply and are insisting on new...
Replies
1
Views
362
Hi all, it's been a while since I've been on, apologies. I am debating whether I need to replace the bonding to the gas meter. The meter is...
Replies
1
Views
280
Hi Guys Would I be correct in thinking an electric cable can be as close as 25mm to a gas meter ? (not that I'd ever be that close out of...
Replies
4
Views
702
I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
603
Hi everyone, a landlord is converting a house into two flats and wants a separate consumer unit for both flats upstairs and downstairs. He also...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock