Hi there.
just to confirm my thoughts.

on fitting an external floodlight 400W into to the lighting circuit of a bungalow, what tests do you guys do?
R1+R2 on all light fittings and sockets for proof of earth and values?
Insulation on that whole circuit, if I can remove all bulbs, or lives/earth if not?
ZS on that whole circuit If I have found the furthest point?



Many thanks for your replies
Spikenaylor
 
you only need to test the circuit you work on. IR, R1+R2, Zs, ensure earthing and bonding in place and adequate. MWC.
 
If you have sensor on the flood light dont carry out an IR test you might blow the circuit inside it, but you R1+R2 and Zs should be ok.
 
good point. if in doubt, short L/N and IR to E.
 
The cable comes through the wall straight into the back of the light. So the light has to be of a type where it can accommodate the cable and terminations inside its own housing, without either being visible.

Therefore no "external" cable or terminations. Thus, NOT notifiable.
 
The cable comes through the wall straight into the back of the light. So the light has to be of a type where it can accommodate the cable and terminations inside its own housing, without either being visible.

Therefore no "external" cable or terminations. Thus, NOT notifiable.


As it is a floodlight I think you will find there are external cables.
 
Therefore no "external" cable or terminations. Thus, NOT notifiable.

external cable is not notifiable as long as it's fixed to the fabric of the building and doesn't have any terminations apart from the light it is supplying.ot
 

Reply to External light testing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
574
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Hello all, I know this is very simple but I would like some advice please. I am installing a new circuit to feed 5 external floodlights. It is...
Replies
7
Views
3K
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
522
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
372

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock