Hi,

I need to run a spur from a main ring socket, however, it already is supplying a spur ( double unused socket ). Is the only way to disconnect the unused spur? Or can I incorporate a fuse? What's the safe way to do this please?

Screenshot_20230205_213151_Samsung Notes.jpg

Thanks
 
Screenshot_20230205_213151_Samsung Notes.jpg
 
best compliant way is to fit a 13A FCU befor the sxisting spur sockket,then daisy chain from that socket to however many more sockets you need
 
As above, or a fused spur between the socket on the ring and all spurs.

Welcome back, Tel
 
If you can run two cables to the new point instead of one, you could incorporate it into the ring. The existing incoming ring cable would be extended through to the new point, then run back to the existing socket, where it would rejoin the existing ring, and pick up the existing spur too. That is the best configuration.

If you cannot run two cables to the new point, then we must re-open the debate about taking two unfused spurs from a single point, or rather from two very closely adjacent points. This has been discussed not long ago in a very contentious thread, where a specific configuration was proposed to bypass the intent of the regulations while claiming to comply with the letter. There have also been extensive threads attempting to discuss this point, especially on other forums, which have been derailed by misunderstandings and ignorance.

It is often pointed out that you can feed any number of points from a fused spur, i.e. where a single fused connection unit in the ring or spurred from it, feeds a radial with unlimited points with a maximum load of 13A total. To use this method in the OP's situation, both the new and the existing spurs would need to be fed from the FCU, not just the new one. However, although compliant, I consider this to be an inferior arrangement because the maximum load is even less than available from one (compliant) double point on an unfused spur, and there is a possibility of the 13A fuse in the FCU being subjected to long, low overload which is undesirable due to the tendency to cause heat damage.

Suppose there were two existing points in the ring next to each other; it would be technically compliant to take one spur from each. It might be poor design if one could foresee that both spurs would have heavy loads, as a significant load would then be concentrated in that area of the ring. However depending on the lengths of the cables and how they affect the load spreading, the loading of the original ring legs might be no worse than if the new points were incorporated into the ring, which would be considered best practice. Therefore, unless one is deliberately calculating cable lengths and resistances to avoid uneven loading, it is hard to argue against adding two unfused spurs each feeding one point.

I therefore suggest that it is not the end of the world in the OP's situation, to leave the existing spur connected to the socket outlet, and to take another spur from a junction / set of Wagos adjacent. I welcome constructive criticism of this approach. Please note that I am not advocating:
  • Feeding two points from one unfused spur (non-compliant as cable is not adequately protected)
  • Connecting two unfused spur cables into socket terminals through which the ring passes (likely to exceed terminal physical capacity, often 3x 2.5mm² max)
  • Feeding known heavy load concentrations (e.g. socket-outlet cluster for dryer / washing machine / dishwasher) in this manner.
 
Another common situation is with kitchen grid switch modules, where the supply for each switch is on the rfc, but each feed off a switch is in essence an unfused spur to a socket for an appliance.

I think I speak for all working electricians that, although fully compliant with regulations, they are an absolute PITA to work on.

Go with Luciens suggestion above and try to incorporate all points into the ring.
 

Reply to Extra spur advice - fuse needed? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
383
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
637
Evening all, I’m looking to install an outside light as a spur from a socket on a ring main. There is already a spur from this socket supplying...
Replies
11
Views
3K
Im running a ring main for all my sockets using 2.5 cable....as an after thought i was thinking to spur off one of my socket outlets and run up...
Replies
4
Views
535
Hello everyone, We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock