Discuss Extraneous parts in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

tigerpaul

-
Arms
Reaction score
101
Supposing I have my Main Incomer (4c70mm2) at one side of a very large warehouse.

My incoming water is on the far side.

My Main Earthing bond (35mm2) is from the incomer to the M.E.T.

I am going to equipotential bond my Structural steel close to the M.E.T. (25mm2)

Can I then come off the Structural steel on the far side to bond to the water incomer?

Or would I need to run a seperate 25mil all the way from the M.E.T.?

How many other services could I use the Structural steel to bond in the same way? Is this acceptable?

Thanks in advance!
 
Surprised no-ones clocked this one...
All incoming services should have their own dedicated bond run to the MET.
Reasoning behind it is that say for whatever reason you lost your MET connection to the structure, in your situation by proxy you would also lose protection on the service, in this case the water pipe.
Hope this helps
 

Reply to Extraneous parts in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Recently visited a new build to do a very minor job and spotted a few dodgy looking items so Client asked me to do an EICR. Following items I...
Replies
6
Views
934
Minimum requirements for earthing a steel framed shed? 4x3m As3000 once again giving conflicting advice.. Incoming submain 6mm TPS 2 Core plus...
Replies
3
Views
1K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock