went to job late today 2 new fans fitted with speed controllers working fine until you turn them up to max speed and it trips out. Then the whole site had gone down it hadnt just tripped the mcb but the mccc feeding the db. This happened twice was doing some investigating when the site agent said we had to leave site. got to go back tommorrow and carry on
 
Instyle LED Lighting Specialists UK
This official sponsor may provide discounts for members

telectrix

-
Mentor
Arms
Esteemed
start up current??? or are the fans too big for the OCPDs?? need more info. e.g. what does manufacturer specify ??
 
W

wrinklyazza

  • Thread Starter Thread Starter
  • #3
manufacter specifies dedicated supply which it is on they only pull 3.9 amps on start up and 3.2 amps when there running the controller is rated at 5 amps
 

telectrix

-
Mentor
Arms
Esteemed
so, cable size? OCPD rating? actual current measured with clamp meter?
 
W

wrinklyazza

  • Thread Starter Thread Starter
  • #5
so, cable size? OCPD rating? actual current measured with clamp meter?
Cable size is 1.5mm. The OCPD is a 6 amp type C like manufactor specifies this isn't trippiong the 125 amp is suppling the DB. The current ratings I gave u were taken with a clamp meter
 
W

wrinklyazza

  • Thread Starter Thread Starter
  • #7
Yes the 125 amp is. The fans work ok until u turn them on to full and it just trips
 
K

Knobhead

  • Thread Starter Thread Starter
  • #9
Turn off some of the loads fed from the 125 MCCB and try the fans again.
 

Marvo

-
Mentor
Arms
Esteemed
Could be just coincidence, I would be probably be looking elsewhere for the tripping problem if they're 3A fans on a 125A MCB. If it's not overloaded check the terminations aren't getting hot and check the main neutral terminations.
 
K

Knobhead

  • Thread Starter Thread Starter
  • #11
I think we’re only being told a part of the story Marvo. As per usual.
 

Reply to fan tripping breaker in the Electrical Forum area at ElectriciansForums.net

Aico Carbon Monoxide Detectors
This official sponsor may provide discounts for members

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Bulk Workwear - Clothing Suppliers for the Whole Forum Network
This official sponsor may provide discounts for members
Top Bottom