Discuss fan tripping breaker in the UK Electrical Forum area at ElectriciansForums.net
W
wrinklyazza
went to job late today 2 new fans fitted with speed controllers working fine until you turn them up to max speed and it trips out. Then the whole site had gone down it hadnt just tripped the mcb but the mccc feeding the db. This happened twice was doing some investigating when the site agent said we had to leave site. got to go back tommorrow and carry on
start up current??? or are the fans too big for the OCPDs?? need more info. e.g. what does manufacturer specify ??
manufacter specifies dedicated supply which it is on they only pull 3.9 amps on start up and 3.2 amps when there running the controller is rated at 5 amps
so, cable size? OCPD rating? actual current measured with clamp meter?
check the other loads on it. could be on it's way out.
Could be just coincidence, I would be probably be looking elsewhere for the tripping problem if they're 3A fans on a 125A MCB. If it's not overloaded check the terminations aren't getting hot and check the main neutral terminations.
Reply to fan tripping breaker in the UK Electrical Forum area at ElectriciansForums.net
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Hi all, I have been on a site repairing damage caused by travellers collecting copper for the last week. We have found and replaced cabling to get...
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...