Discuss Fault advice in the UK Electrical Forum area at ElectriciansForums.net

Ross1

-
Reaction score
16
Evening guys,

Been to a customer today to investigate a fault that they have had for over a year now.

When the cooker/hob is on then they are getting a tingle on the taps and in the shower. didnt have much time today but can tell you that water pipes in bathroom and the boiler area are all bonded back to the MET. the cooker, boiler and lights are on the non RCD side of board.

Hate fault finding, has anyone got any tips for me to narrow it down quickly.

thanks
 
I'll have a guess;

The Cooker is the source of the fault, you should be able to pin down which hob it is by tingle testing with one on at a time.

(disclaimer, extemely bad method of testing, but no worse than walking away and leaving a potentially dangerous situation, the cooker should have been isolated, takeaways are cheaper than funerals)
 
as its the cooker then an ir should show an earth fault on the circuit testing it would hopefully be the switch end but more than likely the main run is damaged
 
PAT testing the cooker will show up any wayward leakages......

Now how many people PAT test fixed/hard wired equipment ?

However, any leakages on the elements, which is quite probable, should be dealt with by the cooker's cpc.

Edit:
Now, if the installation was TT with no RCD, or even with an RCD, the potential on the MET would rise to the difference between the applied voltage and the volt drop across the cooker's element.
If the TT Ra (Zs e) is high, then the voltage might well be high on the MET..... Just a thought...
 
Last edited:
PAT testing the cooker will show up any wayward leakages......

Now how many people PAT test fixed/hard wired equipment ?

Funny you should say that actually lol
Lots of my fixed/hard wired equipment now has various single and 3 phase plugs on and I've made various assortments of sockets to plug them into which then plugs into my PAT tester............so easy to do as well :)
 
Just like to add a bit more......

Local supplementary bonding will reduce the possibility of shock particularly when completely wet in a shower.

However an RCD alone may not provide the necessary protection as you are hanging onto a metal shower head, or possibly not, while standing on a metal bath.
I don't think the enamel or a metal shower water drain, or not, will provide enough IR not to provide a few mA of circulating current.

I think standing wet in a shower with 5mA of current circulating would be enough to tell me something wasn't right.....

SO much for 30mA RCDs, never mind the 100mA up front RCDs installed on some TT systems
 
probably been cooking too many horse lasagnes. trigger's revenge.
 

Reply to Fault advice in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
One of the oddest jobs I've ever had today. Called by a plumber I know who had attended after a leak through the kitchen ceiling from bathroom...
Replies
24
Views
6K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K
Hi, working in a property a couple of years old. Earthing System is a TN-C-S. Customer’s daughter/wife have both complained about receiving a...
Replies
16
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock