Diib I now that lol just been working out thermal constraints on my design protect and noticing the lower the zs the higher the fault current was wondering if anyone could explain why other than ohms law
 
Diib I now that lol just been working out thermal constraints on my design protect and noticing the lower the zs the higher the fault current was wondering if anyone could explain why other than ohms law

Hey, think basic maths.....230V/23ohms = 10amps...... 230V/230ohms = 1 amp, notice that the larger the figure you divide by, the lower the answer..its really that simple .....ohms law;)
 
as above. current is inversely proportional to resistance, voltage being constant.
 
So if are zs are to good ie a very low impedance surely are high fault current could possibly be dangerous

You're looking at this from completely the wrong direction, if there's a L-E fault you want a low earth impedance for two reasons, firstly to prevent the chassis of fittings and appliances developing high touch voltages which could cause someone to get a fatal shock, secondly a low earth impedance means a very large fault current flows which in turn means the OCPD disconnects the faulty circuit very quickly.
 
But with very low external impedance, comes rather large fault currents which may cause a few problems with your earthing conductor and the breaking capacity of your ocpd's
 
Really, I think you'll find the general B type breakers are 6kA, although with back up protection of your main fuse you'll get away with up to 16kA
 
Well all the MG ones we use are rated for 10kA anyways :p
Granted there are 6Ka out there to :p

As a general rule of thumb nearly all breakers designed for 3 phase DBs are 10kA, and nearly all designed for domestic CU ranges are 6kA. You will get interchangeability with most manufacturers though.
 

Reply to Fault current in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
699
Hi all Was looking in to the adibatic equasion as our company will not let us add on to a Ring circuit with 1mm cpc.. I want to give some...
Replies
12
Views
1K
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
498
Hi all, I have a question regarding the breaking capacity of circuit protective devices. So, the breaking capacity rating of devices in domestic...
Replies
13
Views
3K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
438

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock