I had a 10 minute look at an existing fault yesterday as walking out of a customers house as it was way past beer o'clock, the circuit is from a dual RCD board. Serves lighting in a loft conversion with balcony (outside lights) en suit, downlights shaver socket, bathroom fan and central pendant.

Tested IR which was very low at 13.44MΩ between joined live/neutral and earth and no continuity on earth and neutral and live conductors.

Energised circuit and everything was fine, then decided to test RCD and then the circuit tripped the RCD, both RCD's are ramp testing okay. Now continuity shows resistance between live/neutral and earth around 66Ω.

Thinking a nail through a cable/neutral fault somewhere but trying to work out in my head why it all energised okay and then tripped and fault re appeared during the RCD ramp test? Any suggestions or previous experience of this from anyone? (Going back monday morning!)
 
Sorry roly, being a bit thick. Can't understand your post. Circuit energises, but when does the RCD trip?
Tested it as the customer stated it was tripping and although low readings tested out okay. I then energised and all was okay, lights came on etc. I had moved the lighting circuit to the second RCD as thought the first may be dodgy so then ramp tested both RCD's. After ramp testing the RCD's the fault re appeared, definitely a neutral fault, just trying to work out the link between the ramp test and fault or just coincidence?
 
Last edited:
Could be an ordinary intermittent fault i.e. something just about touching, varying between the two extremes you got. 66Ω could be something just barely touching metal-metal, or could be a fault in series with a load. If it's unstable, it's probably an intermittent, if it's stable it's probably through a load. In that case the 13MΩ may have been with the load switched off and 66Ω with it on. I don't see a direct connection with the ramp test other than that you energised the circuit.
 
Found an untraceable core of a three core and earth which had been earth sleeved and put into the earth bar, as soon as I removed it all the IR results shot up!? Then immediately found a neutral core which had been shorting on a back box, could have been either but by that time had lost the will to live and decided not to try to replicate it!:)
 

Reply to Fault on lighting circuit - What am I missing? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Replies
11
Views
1K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
405
Hi I know I have to do more testing but I just want to see if there is something I’m missing. Customer said light fitting in the loft was...
Replies
11
Views
1K
Hi There is a lighting circuit fault in a property with the downstairs lighting circuit. I have tested the voltage and there is 230v on both...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock