Domestic installation, rcd tripped on supply to garage which then feeds a barn 25 metres away via swa. supply cable to garage is swa and tests out fine on insul res and continuity as does swa to barn. connect any load to con unit in barn even with no earth and rcd trips? Circuits in barn show healthy insul res readings? any ideas chaps?
 
ran out of time today will try tomorrow, seems strange that with good insul res readings the rcd trips even with a pendant connected across supply?
 
Well an rcd test will take the guess work out.

did you carry out all IR tests?

L - N, L - E, N - E

Is pme exported?
or is it on a seperate spike?
 
Is this a brand new installation, or an existing one that has mysteriously started to have this problem.

If it's new, it sounds like a neutral in the wrong busbar, or neutral link not taken out between busbars in an RCD consumer unit.
 
its an existing installation with a new 17th edition twin rcd board bin added, yes insul res tests done between all conductors?
 
as others have said do a ramp test on the rcd. If all is well try disconnecting each circuit individually and then loading the installation to rule out the possibility of parallel paths.
 
yeah test button is functioning

That is NOT how you test an RCD.

The test button is a very basic functional test.

From the sound of it "someone" has done a board swop and mixed up the neutrals.
That "someone" also has not done the required tests on the existing and the altered installation.
 
check also the manufacturers internal tails in the CU. it is not unheard of to find an incorrect connection.
 
Anything plugged in?

Got called back to a CU change, which I had completed on Friday, on Saturday morning - customer had tripped the RCD when plugging in a 4 way extension. I took the cover off the plug of the extension and the N-E were reversed. He did look a tad embarrassed!
 
neutral connection for a lighting cct found to be in the wrong bar on investigation, have done new checks for customer and circuit is behaving itself. rcd tests were o.k. thanks
 
Faulty rcd? {filename} | ElectriciansForums.net
 
That is NOT how you test an RCD.

The test button is a very basic functional test.

From the sound of it "someone" has done a board swop and mixed up the neutrals.
That "someone" also has not done the required tests on the existing and the altered installation.

if the test button wasn't functioning would you class this as a satisfactory condition for an rcd? i think not!!!

I was doing a test the other day on a council property changed main s/w for an 80A / 30mA RCD as soon as the starter on the 2d or 5ft fluorescent fitting tried to fire the rcd would trip. Ir tests showed no problem but on a ramp test the RCD wasnt tripping untill 150mA also the test button wouldn't work! I swapped the rcd still the same problem, with the rcd isolated from all final c/cts the test button would work! it turned out to be a parallel path for the neutral with there being 2 supplys to the flat , 1 being economy 7 and with there being only 1 terminal for neutral in the time switch for the immersion and night heating whoever fitted it just doubled them up. So I would say checking the test button might not be a bad place to start as I'm sure you would do this anyway as part of testing???
 
if the test button wasn't functioning would you class this as a satisfactory condition for an rcd? i think not!!!

Indeed it is not a satifactory condition. My response was as a result of the interchange relating to if the RCD had been tested and the response was
yeah test button is functioning
.

If I remember my training, the RCD is tested re ½, 1x and 5x the nominal op current as part of the live tests. These results go on the cert. The working of the test button is a functional test. and (again if i remember my training) the functional test on an installation is the very last thing that takes place after all the other dead and live tests have been carried out.

I agree, an RCD will be rejected if the test button does not work because that is the user's only belt and braces method of knowing that the RCD functionally works.
 

Reply to Faulty rcd? in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock