revolt3k

Cant seem to find it now, could somone remind me of the following when carrying out the schedule check list.

1. Presence of earthing arrangements for combined protective and functional purposes

2. Presence of adequate arrangements for alternative sources where applicable

3. Choice and setting of protetive and monitoring devices (fault or overcurrent protection)

Segregation of saftey circuits. <- Fire alarms and alarms etc ?


Many Thanks in advance
 
Hi.

1. This is extremely rare and you would not come across it in a domestic situation (all to do with high protective conductor currents and how they are filtered out) so an N/A in the box.

2. This is only applicable if you have a back up system such as a generator or UPS setup, again for domestic usually N/A

3. You should really know this one mate as it's all to do with selection of the correctly sized RCD's and MCB's for the installation, so this one gets a tick in the box.
 
Hi.

1. This is extremely rare and you would not come across it in a domestic situation (all to do with high protective conductor currents and how they are filtered out) so an N/A in the box.

2. This is only applicable if you have a back up system such as a generator or UPS setup, again for domestic usually N/A

3. You should really know this one mate as it's all to do with selection of the correctly sized RCD's and MCB's for the installation, so this one gets a tick in the box.


Thanks Lenny ;)
I thought that was what the 3rd one was but would rather check. So Segregation of saftey circuits. <- Fire alarms and alarms etc ? would this be correct mate?
 

Reply to Few more inspection check list q's in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

D
Self Employed Electrician Insurance trying to start off, As you know my English isnt that great so LAWER talk and Insurance sadly i was in the...
Replies
5
Views
3K
DuaneMHunt1976
D
S
Both Basic & Fault Protection SELV – if anything is provided by SELV, this gets a tick, otherwise N/A. Examples would be 12v extractor fan or 12v...
Replies
1
Views
7K
E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
77K
G
Many thanks to ukpablo for finding and posting this in a thread. Thought it would be a useful "sticky.:) Here's a quick guide to what the...
Replies
12
Views
32K
moospark
M
S
hi i have 7 aico EI 156TLH smoke alarms for sale £15 each delivery for 1st alarm is £5, each alarm after the first just add £1 to delivery cost...
Replies
2
Views
6K
super
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock