Earlier I had a 3ph 32amp MCB supplying some 32amp commandos with isolators. They'd then tapped off to a 32amp fused isolator. (To supply another commando socket - I presume for local isolation)
The feed side of this was then supplying a 2w DB supplying a socket off a 16amp MCB. I've recorded the circuit feeding the commandos and then the sub DB.
But it got me thinking.
Should you do a separate (DB) on the cert each time the protective device changes????
 
Earlier I had a 3ph 32amp MCB supplying some 32amp commandos with isolators. They'd then tapped off to a 32amp fused isolator. (To supply another commando socket - I presume for local isolation)
The feed side of this was then supplying a 2w DB supplying a socket off a 16amp MCB. I've recorded the circuit feeding the commandos and then the sub DB.
is this existing ?are you doing a eicr.
 
I only tend to enter a switch-fuse if it is a distribution circuit, is it being used to isolate equipment.
I only tend to enter a switch-fuse if it is a distribution circuit, is it being used to isolate equipment.
possible sub mains ,who knows .
Its not a sub main. It's a fused interlock isolator supplying a 32amp commando socket directly below. A 10mm T and E has been taken out of the supply side to a 2w DB next to it. Main switch and 16amp MCB. This supplies a socket below.

I have recorded on test sheet the circuit supplying commandos and Interlock. The sub main DB supplying socket.

My question is should you record every time the protective device changes.
 
It's not my idea of doing things...…..need a single phase supply so pick up from a local 3 phase circuit point. It should have a separate supply as a single phase circuit....BUT, which regulation gives non compliance?
As regards the DB, it's been taken from a final sub circuit so what is the difference between that and a fixed fused spur.
I wouldn't treat it as separate DB with it's own schedule but make a note on the cert.
Edit. What about rcd with the socket?
 
Last edited:
when and why ?
Isn't that what we do with a DB??? To ensure protective devices will operate within required times???? Fuses are the same??
It's not my idea of doing things...…..need a single phase supply so pick up from a local 3 phase circuit point. It should have a separate supply as a single phase circuit....BUT, which regulation gives non compliance?
As regards the DB, it's been taken from a final sub circuit so what is the difference to that and a fixed fused spur.
I wouldn't treat it as separate DB with it's own schedule but make a note on the cert.[/QUOTE
It's not my idea of doing things...…..need a single phase supply so pick up from a local 3 phase circuit point. It should have a separate supply as a single phase circuit....BUT, which regulation gives non compliance?
As regards the DB, it's been taken from a final sub circuit so what is the difference to that and a fixed fused spur.
I wouldn't treat it as separate DB with it's own schedule but make a note on the cert.
Thankyou
 

Reply to Filling in switch fuses on a certificate in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
773
Hi we have been asked to run a 3 phase supply into a boiler house to feed a DB fed from next to the existing meter. Would we need to install Tails...
Replies
2
Views
751
Since the deco needs doing to this property. My sister needs the TV putting on thr wall but wants the cables hiding. What will be the best way...
Replies
4
Views
338
Hi there, Any advice on this would be greatly appreciated! (Note, this is not a DIY, I'm using a fully qualified electrician, just posting here...
Replies
8
Views
598
Hi all I have been pulled up by Napit, not by my regular inspector. Used rcbo's on a rewire (usually do). Filled out cert to reflect this, with...
Replies
11
Views
692

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock