Does anyone know what regulations or certificates etc may be required to periodically test the functionality of these types of installations?
i used to work for a company and reguarly used to test both of the above in offices and shops etc but was wondering how id go about testing these for myself as it is good repeat work every 6 months
regards
mat
 
cheers lenny,
these are the very same forms i used to fill out on a regular basis. Am i allowed to test these systems or do i need to do the relevant bs course first?
 
Hi.

As long as you are conversant with the requirements of BS 5839, and 5266 and have good liability insurance then you will be ok.
 
Last edited by a moderator:
Electricians can install fire alarms, no probs, as long as you know what your doing! BPFSA run courses, if you dont!
 
Fire alarm systems are a doddle, would like to know more about designing them as with regards to positioning and where devices are required. Which category of system for which type of building etc.
matt
 
Hi Matt, to be up to speed on testing you will need copies of BS5839 part 1 : 2002 for fire alarms and BS 5266 part 8 : 2004 for emergency lighting.
 
http://www.google.com/url?sa=t&sour...3MCdDw&usg=AFQjCNEWa6-iibgVdGzJXAoqjpc-xMPAcg

Hope this helps, i think part 6 is for inspection and testing
 
A site to buy copies of BS for em lighting and fire alarms is linked to in my links at the top of the general forum.;)
 
Part 6 is for domestic type grade systems Part 1 is for commercial type fire alarms.

BS5839:1 2002 states that you should be comptent and examples this by stating you should have relevant experience and qualifcations. e.g a FIA or BAFE course.

Insurance is the big one you need a specialist policy most brokers call it a "alarm maintenance and installers policy" also efficay insurance.

BS5839:1 2002 also states that the maintenance contract must provide 24\7 call out in the event of a fault.

I cant stress enough how this is a life safety system and if you havent got a copy of the regs already and you are thinking about maintaining systems i suggest you go on a course first even after the course you should have a good experience to back you up.

BS5266 for maintaing emergency lighting systems is a lot simpler but still a lot to know regarding the correct placing and type of emergency lighting.

Remember you cannot just maintain these systems to prove if they work. For example if you certificate a system to say 100% of devices tested opperate correctly but you havent checked that there is half of a zone on a four core covering more than 2000sqm and the system fails in the event of a fire i hope you have a good lawyer.

Dont wont to scare you but fires happen and the blaim gets pushed to someone (normally the person with the least backup) look at the nursing home fire in scotland and the recent hotel in newquay.

Any questions let me know.

Adam
 
Last edited by a moderator:

Reply to Fire alarm and emergency lighting testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock