Discuss Fire alarm loop testing in the UK Electrical Forum area at ElectriciansForums.net
Hi all
Just a quick one.
For a fire alarm loop addressable system. Fp200 1.5mm cpc 1.5mm
To obtain R1+R2 would you treat the "loop" as a radial in effect and link brown and earth in connector then tester on other leg.
Or would you treat it as a ring and figure of eight and can be tested at any point.?
Thankyou
It can be handy if trying to calculate length of loop to prove to manufacturer support you haven't gone mad.
In general IR testing is far more pertinent before comissioning.
As you say IR is more pertinent / important to identify any shorts or cable faults
A check of the resistance of each conductor loop will verify that all the connections good and will give a resistance to calculate the loop length don't see the point of the R1 + R2 it's not likely to carry any fault current
Reply to Fire alarm loop testing in the UK Electrical Forum area at ElectriciansForums.net
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Did a check on a ring circuit, due to board having to remain live I did it at a socket.. Was an RCBO, had checked RCD side and all tested ok...