Should a fire alarm be wired in two separate loops one for call points and detectors and a separate for sounders?
I heard this today and wasnt sure it was right, does anyone have any detailed info on how loops should be wired, if there should be 2 loops or all devices on one loop being ok?
 
generally, the detectors and the sounders are totally separate circuits. however, some systems run both on the same circuit.
 
Well this is what i thought, i have installed self addressing systems on one loop, and when i heard that they should be on separate i was like really!
 
On a addressable system, all devices and sounders are on one loop. A loop being the point, starting and returning at the control panel. Isolators are installed every 20 devices are important to the system protecting the loop. This type of system is prefered by most installation companies and is explained full in the BS5839 and does not require sounders to be install on seperate circuits.
 
On an addressable system you can also have seperate conventional sounder ccts,which are seperate from the loop and wired in a radial.This is usually down to cost as conventional sounders are cheaper than loop driven ones.

On an addressable it would be a bad idea to have detection on one loop and sounders on another.If the loop card fails,which can happen no sounders will operate
 
Addressable systems have all devices on the same loop as described above.

Conventional systems have separate detection and sounder circuits.
 
Good point nolnoc, Shouldn`t happen but you never know. Hochiki guild is a great little reference Alarm man.
just a little bit worried here that loop caculations etc will not be done and checked before installation.
 
On an addressable system you can also have seperate conventional sounder ccts,which are seperate from the loop and wired in a radial.This is usually down to cost as conventional sounders are cheaper than loop driven ones.

thats fine on a little system,but if its a big factory etc loop sounders or sounder bases will be way cheaper than running an additional sounder circuit
 
thats fine on a little system,but if its a big factory etc loop sounders or sounder bases will be way cheaper than running an additional sounder circuit


Agreed,if it's a new system. They also leave you limited on strategy.A lot of the time if it's an upgrade existing cabling is used. A sounder control card is sat on the loop and sounders just wired off them.Not a great idea IMO but sometimes needs must
 
Agreed,if it's a new system. They also leave you limited on strategy.A lot of the time if it's an upgrade existing cabling is used. A sounder control card is sat on the loop and sounders just wired off them.Not a great idea IMO but sometimes needs must

fair point,tho if your upgrading from a coventional to addressable your going to have to rewire in some way as it wont have a loop for the detection,you could add a sounder mod to power the sounders but as all the detection will need replaced anyway its better to go for loop sounders
 
Just been to an nursing home today to upgrade a old morley ZXA system today, which might be of interest. I did the usual download was pres 2000 so was in dos (old windows)..check download, a bit narrow over 120 devices on both 2 loops, then checked currrent load on bell circuits 1.5 amps on circuits A and B wow checked out circuits 20 sounders and 20 strobes on each bell circuit which was crashing panel..so disconnected strobes, and now bell circuits now down to 300ma. then tested batteries with ACT meter the 2.1 a/h batteries did not even register total dead. Loop calcs show 12.2 a/h was needed for system. All smoke detection was fitted outside each door at 4 to 5 inches from each door leaving 30m of uncovered space down corridors....so ne panel fiited with 17/H batteries and a V1 form issued for variantions.
his system was fitted over 12 years ago and has been maintained by the same company todate
 

Reply to Fire Alarm Loops? Separate sounder loop? in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock