Hi all please help.
If you was to use galv conduit all the way from the board to the isolator next to the fire alarm panel. does the cable still need to be something like a fp200 or is normal singles ok to use ??
can see the scenario. in a fire, the galv. conduit will get well hot, melt the insulation on the singles. dead short to conduit. OCPD trips. no power to alarm.
Off the top of my head the cable has to be capable of taking 850c for 30 minutes before failing, don't think singles in galv would last that long.
It's common for galvanised conduit to be used for the drops in fire alarm installations. This is for impact protection though and FP200 is still used. 25mm is needed as two FP cables dropping are quite thick.
Try Syrup of figs Mate works very well, so sorry I couldn't resist.
Reply to Fire alarm supply.... in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net
Daughter has bought a house and it has a home security system, G-Tag setup. Issue is the alarm panel displays are pixelated and you cant see...
Good evening! Don’t have a huge deal of experience with fire alarms but having to work on a conventional system at the minute with various...
I'm installing mag-locks and fire door hold-open magnets at the moment and I'm wondering if any of the cable should be fire performance cable...
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Hi All, Please may I ask if light fixtures must now always be fitted by an electrician? also for domestic homes, is it okay for there to be a...