citadel 2 zone sytem in a bed and breakfast with maybe 20+ heads / split zone 1 down stairs / zone 2 first and small second floor.
no real records / last test 2008
complaint is that the alarm went off twice yesterday (thunderstorms were nearby)
today all leds are flashing every 10 seconds on ALL sensors regardless of zone etc.
reset the sytem and the flashes remain / remove either zone from the panel and the system recognises a fault on the zone pulled .
i feel the panel is at fault but would like your opinions )
or does anybody have the manual for this model (wf senate) FIR-VFPK22SEN
nobody can remember what the panel was indicating when the fire call was raised
i am interested in the way these systems are installed / rules / dos / donts etc
best regards
hi thanks for the info
based on your user name can i ask >
are the makes all intercompatible?
ie tlc brand will work on a senate system?
cheers mike
should be if its a coventional system,just change the eol's for new panel
The system install is a Rafiki twin wire alarm, CB200 made for Senate as Citedel, so unless you replace all detection, the panel will need to be replace like for like with a CB200.
The sensors are ment to flash every 20 secs or so, and when activated led stays lite until reset. Main fault with this system is contaminated detectors, suggest if alarm occurs again, silence panel only, don`t reset, and check which detector`s led is lit and change that detector. Can message manual if required.
oops,didnt see the model number,might need them glasses sooner than i thought,as tazz says if you need a new panel change like for like.
Reply to fire alarm system help in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net
Hi, I need to extend a fire alarm, the panel is a CTEC CFP 2 zone one and currently it has a couple of apollo alarm sense sounder bases/heads on...
4K
Hello People Our Enphase solar system needs to have the AC supply shut down via the fire alarm contactors local input output unit that has NO &...
I am doing renovation to a cafe in Scotland at the moment and after speaking to the local council the building requires the minimum standard for a...
Hi all, I`m hoping someone can give advice how the following will work: I have 1 x C-Tec CFP 4 zone conventional panel i need to link to the...
8K
Good afternoon all, Our company installs fire alarm systems in convenience stores but it's always limited to a conventional system whether it be...