Hi we have a welder which can pull upto 32A according to the spec. It says I(max) 32A.
The circuit to the garage has a 16A MCB at the consumer unit. It's only powering two double sockets however am going to add a commando. So I wondering if 32A MCB would sufficient or would it have to be bigger?

Also there's a local RCD within the garage that 27Amp. Would I not need bigger since it could be switching upto 32Amp? Would I not blow the relay inside the RCD?

The RCD in the garage is just an RCD on it's own with an IP rated casing. It's protecting the sockets on the wall. If I remember correctly the regs says every outdoor socket must be protected by an RCD. So do I buy another RCD unit (an RCD on it's own) or could I use the same one?

I'm currently studying the 2330 but they don't start teaching consumer units properly till level3. Hence why I need some advice. Am told by my lecturer, fitting a commando is the same as a normal 13Amp socket.

I live in the UK.

The cable feeding the garage looks like it's swa cable but am not sure if it's 2.5mm.
 
Last edited by a moderator:
you would need to check the current carrying capacity and installation method of the cable supplying the garage - you can not just up the capacity of an mcb as it may no longer protect the cable :)
 
I don't think am qualified yet to do this so I'm going leave it to our spark. But just out of curiousity, am I not correct the current capacity depends on the length of cable and the thickness of the cable. I just measured up it's half an inch thick so I'm guessing it's 1.5 instead of 2.5.
 
even 2.5mm is not sufficient for a 32A load. you need at least 6mm on a 40A MCB ( supply end ) just for your 32Asocket. add the other loads likely and you're looking at uprating the supply cable to 10mm or 16mm.
 

Reply to Fitting 240V 32A commando in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
1K
Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
710
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
678
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
405
So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Replies
5
Views
719

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock