I consider myself a fairly experienced electrician for my age (22), qualified to 2330, nvq3, am2, 2391 (with a more industrial background) but my domestic fault diagnosis is fairly limited so would appreciate any comments/help on the following situation.

I've come across a single pendant fitting fitted with a energy efficiant bulb that flashes intermitantly when switched off. The circuit is wired as follows:

Pendant is top of stairs & switched from 3 locations (2 way at top & bottom of stairs & an intermediate at one end of the landing). Normal loop in/out arrangement in the rose. No junctions/alterations evident.

I have changed all switches as a matter of course (as they're around 15/20 years old) as a potential source of the problem. I've carried out insulation resistance testing across all conductors in the circuit which all confirm good readings.

When checking the voltage present to the switch return in the ceiling rose when switches are off (in every possible comination) a reading of around 30 volts is gained. I guess this 30 volts is enough to allow the energy efficient bulb to flash now & again.

Can anybody shed any light on the subject? (bad gag) any suggestions of further testing i can carry out?

Many thanks
 
Ah yes, the old induced voltage in the strappers issue.

There are a couple of threads on here regarding this issue, I'll see if I can find them.
 
yes polarity was checked ealry on when i found this 'induced voltage'.

But thanks for the heads up.

I think after reading through lennys suggested threads i'll try a different buld first. It seems odd though that for 20 years this has never been a problem, i can only assume the customer had been using old GLS lamps in the pendant untill now & the effect was either less or non existant with GLS lamps ...
 
This phenomenon is caused by the final circuit cable capacitance. It is more common in conventionally wired two way and intermediate switching circuits due to the wide spread use of 3+E cable and the extra parallel capacitance that creates.
The CFL lamp is essentially a fluorescent tube driven by a high frequency oscillator powered by a mains rectifier and smoothing capacitor.
Even though the live feed to the CLF is switched OFF the cable capacitance allows leakage current to flow to the CLF slowly charging the smoothing capacitor in the CLF until the potential is sufficient for the oscillator run and "fire" the CLF tube. This discharges the smoothing capacitor, the oscillator stops, the tube extinguishes and the process of charging starts again ... if conditions are suitable this continues indefinitely.
The problem may be temporary however, only occurring shortly after switch OFF, when the gas in the tube is warm and more easily ignited. As the gas cools ignition become increasingly difficult, the energy from the oscillator become insufficient to heat the filaments and ignite the gas in the tube before the smoothing capacitor becomes discharged.
A simple solution is to permanently discharge the cable capacitance by wiring two 160K ohm, 1/4W, resistors rated at >=250V, in series across the lamp holder terminals. Do not try to use a single 330K ohm resistor because this may fail due to voltage breakdown.
If this solution is implemented a notice should be placed at the DB stating which final circuits are effected and which lamp holders have been modified and how.
A conventional GLS filament lamp doesn't suffer this problem because the filament is permanently loading the cable capacitance and any acquired charge is unable to overcome the thermal inertia.
 
Last edited by a moderator:

Reply to Flashing Light bulb when switchs are off... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K
Hi all, No change to electric wiring and supply and no change to the previously working light bulbs but now when I turn the 2 wall lights in my...
Replies
2
Views
975
Good afternoon everyone. I have fitted an extractor fan in my bathroom with an overrun timer, to start when the bathroom led lights are turned on...
Replies
92
Views
8K
Hey everyone, here's my imaginary problem, let's say I have 2 light bulbs, both of them take energy from the same source, however, 1 of them has a...
Replies
3
Views
1K
Driven by the recent colossal hikes in the cost of electricity I hit upon the wizard wheeze of replacing some of the existing LED bulbs in our own...
Replies
2
Views
911

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock