Changing a consumer unit at a flat but have a few questions regarding earthing etc. supply is from 16mm T&E fed from the incoming supply cupboard in a separate building main supply is tn-c-s. Each flat is supplied from a 63amp switch fuse. So earthing to the flat is via the 6mm back to the switch then 16mm back to main supply ze measured at 0.16 at switch and 0.20 at CU.
Flats are bonded in 6mm.

What are regs in regards to bonding from switch tto board? Being a TNCS should it not be 16mm back to supply? Only trouble being its impossible to do this?

I haven't done many changes in flats and wondered what the ddeal with supplies as regs?

Thanks Ian
 
Wetroom Store - Network Wetroom Suppliers
This official sponsor may provide discounts for members
Changing a consumer unit at a flat but have a few questions regarding earthing etc. supply is from 16mm T&E fed from the incoming supply cupboard in a separate building main supply is tn-c-s. Each flat is supplied from a 63amp switch fuse. So earthing to the flat is via the 6mm back to the switch then 16mm back to main supply ze measured at 0.16 at switch and 0.20 at CU.
Flats are bonded in 6mm.

What are regs in regards to bonding from switch tto board? Being a TNCS should it not be 16mm back to supply? Only trouble being its impossible to do this?

I haven't done many changes in flats and wondered what the ddeal with supplies as regs?

Thanks Ian
Just out of interest, is the 16mm T&E from the main building protected in any way?
 

Taylortwocities

-
Arms
Esteemed
<HINT>
Your supply type might be tnc-s to the switch fuse, but what is the supply type from the switchfuse to the flat?

The Neutral and earth are no longer combined...................:wink5:
 
S

Snapester

  • Thread Starter Thread Starter
  • #4
Yes im hoping so I think it's ducted under the building it's about 30yrs
old.
I see what you are saying the supply is now essentially TNS?
 
S

Snapester

  • Thread Starter Thread Starter
  • #5
So bonding in the flat can be 6mm if the supply is classed as TNS?
 

Amp David

-
Mentor
Arms
I'd check that the 4mm earth to each flat is ok too.

Surely the earthing is still TN-C-S though

Bonding is 10mm for your earthing system. Its only like putting a sub main into an outhouse or similar that has ECP in it.

One reason not to use TandE for submains, its nasty:furious3:
 
S

Snapester

  • Thread Starter Thread Starter
  • #9
Working with t as 0.1 on equation CSa of protective conductor works out at min of 4mm so 6mm will suffice for installation.
Can bonding stay as 6mm as its a nightmare to change in this flat? Noted as a departure?
 
G

Guest123

  • Thread Starter Thread Starter
  • #10
Quoted from ESC guidance......

Q12. When carrying out electrical work on an installation forming part of a TN-C-S system, is it necessary to upgrade existing 6 mm² protective equipotential bonding to 10 mm²?
Not necessarily. If the existing 6 mm² bonding connects all the extraneous-conductive-parts to the main earthing terminal, has been in place for a significant time and shows no signs of thermal damage, then it may not require to be upgraded.
 
Quoted from ESC guidance......

Q12. When carrying out electrical work on an installation forming part of a TN-C-S system, is it necessary to upgrade existing 6 mm² protective equipotential bonding to 10 mm²?
Not necessarily. If the existing 6 mm² bonding connects all the extraneous-conductive-parts to the main earthing terminal, has been in place for a significant time and shows no signs of thermal damage, then it may not require to be upgraded.
This is always the excuse people give for not upgrading any installation tho..... "It's been working fine like that for years". :)
 

Reply to Flat consumer unit change. in the Electrical Forum area at ElectriciansForums.net

Wetroom Store - Network Wetroom Suppliers
This official sponsor may provide discounts for members

Select the ways in which you gain online business

  • MyBuilder.com

  • Federation of Master Builders

  • CheckaTrade.com

  • RatedPeople.com

  • TrustaTrader.com

  • Which? (TrustedTraders.Which.co.uk)

  • MyJobQuote.co.uk

  • Yell.com

  • Google Paid Advertising

  • Own Website with Natural Ranking (SEO'd website)

  • Social Media (Facebook Twitter Instagram etc)

  • Word of Mouth Only for me


Results are only viewable after voting.

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Electrical2Go - Online Electrical Supplier
This official sponsor may provide discounts for members
Top Bottom