BruceB

-
Arms
Reaction score
142
I have been asked to quote for about 7 kW PV on a single storey commericial building in a town. The x4 roof areas all slope at about 10 degrees to the horizontal. It has many characteristics of a flat roof rather than a pitched roof (no apex). No time for planning permission so want to meet non-domestic PD rules. A pitched roof means I can come 200 mm from surface; a flat roof means I can come a metre above, which might be useful for an east/west array.

Has anyone seen any guidance on (or got any experience of) how sloping a roof has to be to no longer be considered flat under SI 2012/748?
 
Last edited:
Hi Bruce,

Any roof with a pitch less than 5 degrees is considered flat in the BSEN1991 and the BS6399 therefore the roof with a 10 degree pitch is a pitched roof.

If you need any structural reports (includes static, wind & snow loads) please do not hesitate to contact us.

Kind Regards,

Bryan McGrory
BMG Surveys Ltd
BMG Surveys Ltd. - Home
0141 532 2322
 
They are permitted development and have been since March 2012, subject to 50kWp limit and other parameters.

On 25th March 2015, non-microgeneration (>50kW) then also got a load of dispensations and so also got permitted development, subject to a load of conditions.
 

Reply to Flat roof or pitched roof? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

F
I'm pricing on a factory for 50kWp install with 7 degree slope but east west facing roof. I was wondering if it was feasible to install a flat...
Replies
15
Views
3K
finchy
F
A
I've looked through various other threads on flat roofs, but to no avail... We've been asked by our friendly Buidling Control Officer to quote...
Replies
5
Views
2K
daytona600
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock