Help. I have a real problem. My electrical supply to my house is doing the weirdest of things.
When the diswasher is on the lights around the whole house dull right down. However if i then put the kettle on normal service is resumed. By mistake i cut through an earth cable but repaired that. Would it still be that ? Some said it may be an arc but how do i test for that . I have put a martin dale tester over the sockets and they are all ok. Please help!!!!
 
Hi

Sounds like a loose connection, or could be VD drop, not sure why its ok when the kettle goes on. at least you can think about it over a cup of tea..

Welcome to the forum

Regards Electro
 
Help. I have a real problem. My electrical supply to my house is doing the weirdest of things.
When the diswasher is on the lights around the whole house dull right down. However if i then put the kettle on normal service is resumed. By mistake i cut through an earth cable but repaired that. Would it still be that ? Some said it may be an arc but how do i test for that . I have put a martin dale tester over the sockets and they are all ok. Please help!!!!
What earth cable did you cut through and welcome to the forums
 
Last edited by a moderator:
It was the earth on to copper pipes! Reconnected using a connector block

the earth was going on to the pipework (copper) ..,. could it be i have connected it with a 30amp peice of choc block.. would that be enough?
 
Last edited by a moderator:
Did the problem start following your repair to the earth cable ?

Where about exactly in the property is this connection situated ?

....welcome to the forum...


spark1.
 
Thank you to everyone welcoming me to the forum. I think it co incided! However is now under a shower tray and been tiled over. Thinking of running a new earth to ground spike to see if this solves it or it is more major!is there a test i can do?

Thank you to everyone welcoming me to the forum. I think it co incided! However is now under a shower tray and been tiled over. Thinking of running a new earth to ground spike to see if this solves it or it is more major!is there a test i can do?
 
Last edited by a moderator:
jedi ,mate I think you definately need some further inspection & testing on your electrics ...You need to verify that your incoming supply to the consumer unit is o.k with particular reference to the neutral conductor...plus an insulation resistance test on all your outgoing ways from the c.u. If you are not competant to do this yourself then arrange for a qualified spark to carry out the tests iam sure he will find the true nature of the problem for you.


spark1
 
Earth spike may introduce a different potential in the house are you on a tt system already. If not a spike not really recommended

Welcome


Chris
 
Not sure at all if Im in right ballpark but we had a job with flickering lights to fault find a short while ago. We traced a fault to a loose Neutral in the living room light fitting. However, lights throughout house still flickered. A Ze was recorded at distribution side & found to be that, (can't remember figure) but EON came out & sorted it...I'll post a reply after asking Boss tomorrow am
Cheers
 
Not sure at all if Im in right ballpark but we had a job with flickering lights to fault find a short while ago. We traced a fault to a loose Neutral in the living room light fitting. However, lights throughout house still flickered. A Ze was recorded at distribution side & found to be that, (can't remember figure) but EON came out & sorted it...I'll post a reply after asking Boss tomorrow am
Cheers


Along the lines of what i was referring to in my earlier reply.

If the supply is TNCS then the Neutral& Earth are one and the same on the supply side.....a loose main neutral connection can allow return curent from circuits to flow to earth through extraneous conductive parts such as metallic pipework etc...part of this path could well be the earthing cable the o.p. "repaired", hence my advice to get it tested a.s.a.p. :eek:


spark1
 
Last edited by a moderator:
Total agreement with spark 1 the sooner you get it checked the better.
If it is a loose neutral it can cause major heat damage to surrounding components, and if its at the mainswitch termination that won't take long.

Glad its only single phase though,
I have seen the results of a lost neutral in a three phase install, on single phase equipment, and its not a pretty site.
We spent days after rectifying the fault on replacing lighting, hand dryers, fire alarm panels, door entry systems, the list can be endless,as well as expensive.

Get it checked A.S.A.P.
 
As it is affecting more than one circuit I would check connections in CU and look carefully for signs of hot tail connections. Then try a ELI test at the incoming mains supply this may show a high or unstable reading if so I would get DNO out to check supply. Are you overhead or undergound fed, as overhead supplies often suffer from bad connections underground do but it is less common.
 

Reply to Flickering lights! in the Australia area at ElectriciansForums.net

Similar Threads

Hello all- I hope this is the right place to ask this question. A few weeks ago the LED lights in the kitchen started flickering intermittently...
Replies
2
Views
654
I am not an electrician but am looking for some advice as to how to fix my sporadic light flickering problem that has come and gone for the year...
Replies
24
Views
2K
My son is having a new house built. The electrical wiring is almost complete but a problem has been detected. Some of the rooms LED lights...
Replies
3
Views
1K
Evening All, Strange one so after a bit of advice. Got called to a customer this evening who had their boiler repaired after the circuit board...
Replies
4
Views
1K
Hi all, just joined the forum, have a weird problem, wondering if I could get some ideas. We built our house about 6 years ago. The downstairs...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock