I have fitted underfloor heating, using a WarmUp Wifi thermostat.
When i turn it on, the RCD trips after 5 seconds on initial turn on.

I have measured the following;
Live - Neutral - 39 Ohm (expected for size of mats)
Neutral - GND - >1M
Live - GND - ~150k

Now the L-G resistance of 150k seems unusual. I would expect either infinite or a direct short?

I did notice that the plasterer had slightly nipped one of the wires, but it seemed as the sleeving had just come off?

Any ideas? 150K is not ideal, but could it just be that the RCD isn't sufficient for the power required to power the mat?
Any help would be appreciated, would be devastated if it doesn't work, a lot of money and hard work down the drain!
 
sounds Like the heating mat has been damaged during installation, ideally you would be looking at insulation resistance measurements of >200M ohms between line conductors and earth
 
Yep, also what type of flooring has been laid on top of this? Was he heating mat tested once unpacked and also once laid before any flooring work carried out?
 
When I fit these I test straight out of box, once laid just before next stage of flooring carried, connect my monitoring device while other flooring works carried out then test again before my connection and commissioning stage
 
When I fit these I test straight out of box, once laid just before next stage of flooring carried, connect my monitoring device while other flooring works carried out then test again before my connection and commissioning stage
That is the way it should be done . Test at every stage and save that sickening non event.
He did not reply if the installation results were OK.
Hopefully the nick in the cable and damp plaster may be the problem.
 
Not normally plaster on the floor, well not withstanding those plasterers do slop it about :)

Wonder if the floor tiles ben laid? @Jamie Harper there are some companies who suggest they can locate such faults, if your floor tiles are expensive ones.
 
I was thinking damp plaster in the chase for the receiver lol.
I just guessed that is where the cable is nicked. :)
 
I was thinking damp plaster in the chase for the receiver lol.
I just guessed that is where the cable is nicked. :)
if it is it's only a tail and could easily be repaired.
 
Hi all, sorry for the late reply, i wanted to ignore it over Christmas! But i am back to figure out this issue!
So in response, i did check out of the box and everything was okay.
It appears to be where one of the wires (heating) have been nicked ever so slightly.
Now i can not access the floor, as it has 2 layers of self level, underlay and laminate on top, so no way of fixing the issue directly.

I have, however, had an idea, which I would like an opinion on.
This may be controversial...

Now the issue is only between Live and Earth, as we have established.
So do i actually need to connect the Earth from the mat to the thermostat?
I understand that earth is required for safety/fault conditions, but the whole mat is under self level, with no way of getting to it (unless drilling through the floor).
I know there will be some unhappy people for even considering this, but I can not see any reason to why not connecting the earth to the mat would cause any issues UNLESS i was to drill through into a wire for instance.
[automerge]1578318555[/automerge]
Hopefully it’s nicked in the cold tail between floor and wall so should be a reasonably easy fix
unfortunately not, it was the heating wire that was nicked....
 
You say 'the issue is only between live and earth'. This is the most crucial one unfortunately.
 
You say 'the issue is only between live and earth'. This is the most crucial one unfortunately.
But i do not connect the earth to the system, the fault does not exsist? what harm can this cause? It is a closed system effectively, the wires are in the floor with no chance of touching them?
 
I know what you meant, but it is not wise to remove the earth on a known faulty circuit. Especially in a bathroom.

Out of interest, why did you bother testing if you were going to ignore the dangerous results anyway?
 
Status
Not open for further replies.

Reply to Flooring Tripping RCD in the Electric Underfloor Heating Wiring area at ElectriciansForums.net

Similar Threads

Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K
m having a bit of an issue that is proving difficult to resolve. For 2 years I have been having no problems with my setup. I have a 3 zone house...
Replies
1
Views
1K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
I have a customer that has 3 heating mats under the tile. This was installed a while back and a relay was used. I measured a 21 amp draw for all...
Replies
4
Views
2K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock