ive just purchesed a new fluke 1653b multi tester when taking a eath fault loop reaqding on loop no trip setting i get a differant readng to when i take a reading on the hi current setting is this meter faulty
can anyone help the readings i get on the same 32a ring socket are

notrip setting 0.64

hi current setting 0.50

as you can see on the nontrip setting is higher and woulld fail as max is 0.58
 
Don't think you have a fault. I have done the same experiment with various meters and always get a higher reading when using the low current test.

It's because the no trip test uses a very short pulse and the RCD has significant inductance, so the observed figure is higher.
 

Reply to fluke 1653b efli readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock