Discuss Fluro fittings fused or not in the Australia area at ElectriciansForums.net

O

One_of_them

Hey fellas,

Lighting circuit protected by 10A MCb feeding some fittings in an office. Supply 1.5mm T&E loop in through ceiling roses, flex down to suspended fitting and terminated into a choc block internal of fitting. Out of this choc block is the fittings internal wiring consisting of 0.8mm solid core cable which goes into the ballast. Same wire (but white) coming out of ballast to end caps.

My question is....should these fittings be locally fused to say 3A as the 0.8mm coming out of the choc block is in theory protected by the 10A MCB back at board?

I hope that makes sense and somebody could clear it up for me. Reason....removed some old fittings which WERE fused and fitted new ones which are NOT. I was told some fittings do not require it, is this correct?

thanks in advance
 
If the manufacturer states fittings are suitable to be fused at 10A then whatever size wire it is internally is fine, If they say 6A in there data, then fuse them down. Most fittings have very small internal wiring but you have to remember 0.8mm probably takes more then you think especially in such short lengths.
Go by the data supplied with the fitiings its the only way to be sure!
 
I've never heard of 0.8mm wiring. Is that the diameter of the conductor cross sectional area?
 
It,s likely to be 0.75mm csa. And as above if the fitting is rated less than your circuit protection then yes, derate with a suitable fuse of that rating.
 

Reply to Fluro fittings fused or not in the Australia area at ElectriciansForums.net

Similar Threads

Hi My Kitchen has never had a cooker hood installed. Where the new hood is going to be situated is some distance from any of the outlets in the...
Replies
4
Views
2K
  • Locked
Hi I also posted this on the DIY Electrical Advice - Electrical Appliances Forum My Kitchen has never had a cooker hood installed. Where the new...
Replies
1
Views
687
Hello! Hope you’re all keeping well! I’m replacing a fluorescent tube light which had an electronic ballast fitting - I’ve ripped this out and...
Replies
6
Views
1K
Hi all, Disclaimer: I'm not an electrician and have very basic knowledge of electrical installation. We've been putting in a new kitchen into an...
Replies
17
Views
2K
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock