Well thats an interesting set of figures. Looks like you are going to be putting in a 32A supply. Now it gets interesting, if it can live with a C32 breaker, you are aiming for a Zs of 0.58. However a R1+R2 distance of 50m is going to give a resistance of 0.46 using 4mm SWA, so unless your Zdb is less that 0.12 you wont get it in spec.
If you go 6mm SWA then r1+r2 is going to be about 0.31 which should be good enough, but you need to check the Zdb first before choosing the cable.
If you need a D32 - oh dear suggest move the charging point closer to the DB - LOL.
I would ring the manufacturere or get the installation PDF off the internet and confirm what breaker size they recommend.
Hope this helps