Discuss Fork Lift Charging Point. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

PhilCumbria

Active EF Member
I am currently doing an EICR in a warehouse and one of the circuits is for a Fork Lift Charging point (32A) In Light of the 18th Edition and all circuits being protected by and RCD, should I recommend that the MCB that is feeding that circuit at present be changed to an RCBO ??
 

westward10

In echoed steps I walk across an empty dream.
Staff member
Moderator
You just state the fact it does not have additional rcd protection then it is for the client to decide once they are in receipt of the Report. The 18th Ed does not state all circuits require additional rcd protection.
 

Electrician Talk

Electrical 2 Go - Electrical Supplier and Electrical Wholesalers
Electrical Insurance
ElectriciansForums.net (formerly known as ElectriciansForums.co.uk) was setup in April 2006 to provide free electrical advice to both professional and DIY electricians. Whether seeking advice for auto electrics, trying to find electrical installation condition reports (EICR) form downloads, or whether you're here just to talk to other electricians; we've been a first-choice website for tens of thousands of sparkies for well over a decade.