Hi mate is this job AT MY BRUVS as i am finding similar probs to you
my tutor at college asked me why i tested at both sides of doubles i said because they are both outlets and also value can be significantly higher as i have found
continuity on lighting some switches were giving readings with it switches off
started of at somewhere in the region of well over 4 ohms the meter wouldnt give a constant reading it was as high as 6 some of the time
LOW IR
shower 6mm OK at 45A dp switch feeding 230v fan zone 1 1.0mm / also feeding a FCU for Old C/Heating supply
spurs of spurs
mutiple connection blocks no tape loose connections
hidden JBs with loose connections
rodent damage hidden under a board were i was looking for a hidden JB for landing and loft light were it was giving a high continuity reading
bonding to water after branchwork High readings before and other side
Ip ratings not met on newer single rcd board
circuits still connected in old wylex 4 way going nowhere and about 4 circuits in each
downlights in kitchen 2 supplies switches at side of each other 2.5mm feeding 1.0mm again chockblocks
twiisted Ns not in terminals at sockets
twisted cpcs not in terminal at socket
metal back boxes protruding from wall
grommets missing
no sleeving on earths
switch wires not identified
sockets are suspect to say the least think ring is in JBs most sockets downstairs have 1 cable so spur of JB no prob if not ideal
then spurs of spurs
some sockets had ok reading at one outlet of double socket and at other as much as 2-3ohms
some wouldnt switch off
step 2 and 3 readings are nowhere near within 0.05ohms of each other
cracked sockets and switches with heat damage
every time i found a fault i would repeat the test and slowly but surely reduce the continuity readings to a more acceptable reading and increase the IR
mate i could go on so now like you I test evrything borrowed neutrals even between the disconnected NOW DEAD circuits and the remaining circuits to see if there is continuity still and IR between them
and have condemned the lights and told him unless he lets me under floorboards to have a look its staying locked off as i still have a L-N 0.14 to 0.27 Meg and yes evrything is unplugged disconnected removed linked out
this wouldnt show up if i just tested with L&N joined to earth then i got a reading of
I suspect the lighting problem stems from the 10K kitchne he had done
its not worth 1K
best bit granite worktops the rest any muppet could chuck together
they jsut slung cables behind cupboards and even behind fridge High level double with cables jsut dangling down and disappearing behind cupboards he could of at least used cable clips for 10k
the transformer for pelmet selv lighting is sitting on top of the freezer with untaped chock blocks for the connection point sitting along side the transformer
anyway woooden floors newly laid carpets coming up upstairs and if its bad i will give him the good news lets rewire the lights and sockets LOL and get some chases in the plastering he had done other year lol
Standard British Install Then! LOL